help with Zs. | Page 3 | on ElectriciansForums
Discuss help with Zs. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
There were other similar posts with similar issues and they appeared to come to the same conclusion.
Your were happy with your other results, quality of workmanship and you are using a calibrated tester. You will see the problem when you go back and retest as the others suggested
thats a great Ze 0.08 is the substation in the lounge just for curiosity whats the PFC , does seam a tad low
thats what i thought at first, measured it a few times.
Quite frankly, the only way your going to accurately measure true values this low, is with an EL test kit that has high resolution, these are generally used in sub-stations etc. Or you could use IQ's method that can be found in the ''Stickies'' which is a much cheaper alternative!! (link at bottom of this post) I wouldn't be relying ''directly'' on an MFT loop testing range, be it on the no-trip or full current setting...
You must have a local DNO distribution TX in next doors garden, or very close by anyway... lol!!
LINK....
http://www.electriciansforums.net/inspection-testing-certification-electrical-installations/31838-higher-accuracy-low-ze-test-procedure.html
Found the problem it's the rcd's. next question is would you change them or make a note of it on the test form. would it be ok for the niceic inspector
For the purposes of your EIC you can put your measured Ze and your measured (R1 + R2), and a calculated Zs, Zs = Ze + (R1 + R2), as this is an acceptable method, and will be fine for your assessment.
What is not acceptable is to back calculate from a measured Zs.
....like the new meggar meter gives a value for!!!
do i need to change the rcd's or will it be ok
Changing the RCD's will likely not change your results unless you are changing the manufacturer or type, there have been a few threads on here regarding certain makes of RCD skewing the Zs results.
You cannot realistically replace the RCD's with another make unless you are willing to change the CU.
Your measured Zs will always be slightly different due to either parallel paths or to the 'no trip' setting of your MFT, some MFT's are better than others in this respect.
You can, as I (and others), have already said just put down your calculated Zs results, so long as you have a measured Ze and (R1+R2).
You should not really put a calculated Zs down from anything other than a measured Ze, ie. by enquiry etc.
Reply to help with Zs. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
OLDBOY
O