As already stated...are you measuring at the cooker on the no trip setting?.....this is notoriously inaccurate/random....although the meter manufacturers wont admit it.
 
Is it possible that this is an older PME installation with an MET on top of the service head that has bonding connected and someone has added another MET (EMT) elsewhere? A photo of the service head might help if you had one.
 
What make RCD's are in the board? I'd be tempted to bypass them whilst doing your Zs readings. See what difference that makes. Some makes of RCD have been known to cause problems when trying to use no trip settings on MFTs.
 
Yep, they've been known to have issues. Try linking out one of the RCD's and doing a Zs for one of the circuits then and see if it matches expectations more closely.
 
I have had this happen quite a few times recently aswell.
As some of the others have said try bypassing the rcd. I measured the zs on the supply side of the rcd and on the load side and there was a 1.35 ohms difference
 
Hello mate, you mentioned that you had a di-log MFT. I read that they can throw up some odd readings sometimes, in fact it put me off of buying one. Worth googling to see if its the tester? There is a way round it apparently. long shot but you never know.
 
There were other similar posts with similar issues and they appeared to come to the same conclusion.
Your were happy with your other results, quality of workmanship and you are using a calibrated tester. You will see the problem when you go back and retest as the others suggested
 

Reply to help with Zs. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
316
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
964

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
255
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top