hi have been doing some testing on a existing light circuit usual methos line /cpc linked at board leads and link lead nulled. come accross a very strange problem regurding a R1 R2 reading

Now measuring between sw live and cpc. rose 1/ 0.47 rose 2/1.15 (2WAY SWITCHING) 3 rose 3/0.51 rose 4/ 0.54 rose 5/1.07 rose6/1.97 (2 WAY SWITCHING)

all connections at rose 2 have been checked, switch connections on 2way switching checked, resistance of the actual switches has been measured and switches replaced as i just just thought it was a bad connection giving a false reading,or a high resistance switch but im still getting a high reading which is impossible as the R1 R2 reading at the next rose in the line is only 0.51. Its very strange as the measurment from loop in at the rose to CPC is fine and is as expectected which scuppered my other theory that this rose had been wired out of sequence.

any ideas any one. Just to add when ZS tested readings as expected which again just makes iot stranger.
 
yes totallly agree spark that the longer the switch run the higher the reading but wouldnt the previous switch run resistance still show if all the switches are in closed postion at the next rose or am i missing something simple here its been along day

I think you are confusing your switch lives with your permanent lives.

The switch cable may be quite abit longer (bearing in mind the S/L has twice the distance of the run) than the next roses P/L which is only one length of the run (no return).

Each rose normally has it's own S/L unless both roses are switched from the same switch.
 
Last edited:
Ian,
your S/L's are all only connected to the P/L via the switch cable at one side of each switch, you are effectively measuring your R1 at the other side of each switch at each rose, these are seperated from each other, or else all of your lights would come on together
 
thats a thought one thing i didnt measure maybe its pendant giving a high reading at that point, what is baffling me is the next pendant is showing a lower reading surely this pendant would also be giving a high reading


there could be a connector/ J/B on the switched wire, with loose connections giving rise to Hi R1+R2
 

Reply to hi have a r1 r2 mystery in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
795
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
827

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top