The earthing arrangement and installation method doesn't require 30mA RCD protection for the distribution circuit. The final circuits will be covered by the RCD in the garage board. Having a high integrity board means you can feed the distribution circuit from a non RCD protected way. Doing it this way means you wont have RCD's in series with lack of discrimination. The only discrimination issue you would have would be having to circuit breakers in series of a similar current rating but you'll have to decide if that's going to be an issue and if it is look at a way of providing over current protection for the distribution circuit with a fuse or similar. Are there any extraneous conductive parts within the garage that will require bonding?
That will not provide short circuit discrimination.If values permit fit a c type MCB in the first board , therefore a overload should trip the b type in garage unit fist
That will not provide short circuit discrimination.
No it won't but it will solve overload problems and if plugging in transformer in the garage only the b type will have to be reset not walking back to the house every time
Well it's not my garage , so i don't know . But you agree not to put it on rcbo (two RCDs in series ) so where back to mcbs around the same size . So why not try a c type , for all i know the op could have full set of 110v tools ( plug a transformer in a b type and its 50/50 it will trip ) . Maybe he going to start his own private disco and with the laser light and smoke machine running at the same time OVERLOAD
Are they actually extraneous conductive parts tho? Where have the bonds been connected to? If they've been connected to the earth marshalling terminal in the garage board that is using the TNS earthing arrangement then the CPC of the 4mm armoured cable is not of an adequate CSA to form part of a bonding conductor.
And this is notifiable under part p
Sorry for the delay in replying. At present they are connected to the metal case of the fusebox, to its earthing point and is using the armour of the old 2 core 2.5mm SWA. There is T&E cabling running along some of the frame to the lights, but the earth system seems to work ok as I had one cable pull out of a junction box and touch the frame (clearing out old timber) which tripped the RCD in the house instantly.
The bonds will be connected direct to the new consumer unit as and when I fit it as the old box will be going. But if 4mm isn't enough, I could go up to 6mm.
All the old cabling will be going as well and being replaced with conduit. Actually, everything old is going and will be replaced as this is very much a project.
Thanks, but I was aware of that.