Hi - sorry if you've already seen it @Electro-tech, but for the socket outlets on RFC check out 543.7.2.201 and part (i) particularly. This means outlets need re-terminating etc rather than new cpc needing to be run in. Tin Hat on.
 
We need to know how this leakage has been measured, combined across all final circuits?
Hi Guys, Thanks for the replies. The measured Earth leakage was a combined reading with a Megger DCM300E Earth Leakage Clamp meter on the 16mm cable from MET in the DB. I could not test each circuit as I need to power down to open up the DB out of hours at the weekend. Can't risk knockin a RCD test button while in use.I honestly think that the installation Earth integrity was not designed for IT office use in the first place. I would like to see a 4mm cpc installed .You can tell that the installation overall was not installed correctly going by the T& E runs stuffed in plastic conduit . Main runs are T&E in metal trunking,why not singles. I will measure each circuits leakage separately at the weekend & report back.
 
Hi - sorry if you've already seen it @Electro-tech, but for the socket outlets on RFC check out 543.7.2.201 and part (i) particularly. This means outlets need re-terminating etc rather than new cpc needing to be run in. Tin Hat on.
Okay Wilko noted, but if you have dado trunking while re-terminating the outlets I would like to run the 4mm. The only thing that I do not know at the moment is, are there 1 or 2 earth terminals on the existing accessories?
 
You definitely need to assess each final circuit before deciding on any works as they may not be required.
 

Reply to High Integrity Earthing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
454
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
Just an update for anyone interested, I got another rod in outside today, which has lowered the Zs db to a more healthy 53ohms. The oven elements...
2
Replies
19
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top