Just out of interest, what is it that differs in the article to the information I have provided?
Just out of interest, what is it that differs in the article to the information I have provided?
I'd suggest you look again, at the diagram in the article.The fact that you can put the hi integ earths in the same terminal at the DB as long as they are labelled
Looking at the diagram, terminal 1 has a conductor labled circuit 1 and one labled circuit 2. Terminal 2 also has a conductor labled circuit 1 and another labeled circuit 2.I suggest you read the document again from start to finish, then look at circuit 2 which is a radial, but has the hi integ earth terminated on the same terminal as the cpc of the said radial
Yes the diagram is not very good, but are you seriously stating that you cannot see that the conductors with arrows pointing at them marked 'circuit No 2' are in separate terminals?
The circuits in question are twin and earth 2.5mm RFC's and installed on basket, with no other mechanical path, so IMO this fails miserably
I stated this to the resident tester, and his response was "no no no, there is another reg, " , but indeed he could not quote it.