hi, fitted new consumer in a domestic house.
testing.
ze 0.16
zs at origin 0.04
pfc 6.2ka
the pfc is my problem, ohms law would make the pfc work out around 5.7Ka (using 0.04 as your resistance) (with all paths in place)
using megger 1553 two lead test, high current, pefc and pscc are the same as its pme
im starting to think my meter is faulty, cant think of any other reason for the reading...
i did read if its downstream from 100A bs1361 cutout then effectively if 16Ka breaking capacity, that doesnt really help with mcbs rated at 6Ka
what are your thoughts as ive drawn a blank...?
the pfc just seems too high, its a new (to me) meter, with calibration cert done in jan
thanks for any help