hi, fitted new consumer in a domestic house.

testing.

ze 0.16
zs at origin 0.04
pfc 6.2ka

the pfc is my problem, ohms law would make the pfc work out around 5.7Ka (using 0.04 as your resistance) (with all paths in place)
using megger 1553 two lead test, high current, pefc and pscc are the same as its pme

im starting to think my meter is faulty, cant think of any other reason for the reading...

i did read if its downstream from 100A bs1361 cutout then effectively if 16Ka breaking capacity, that doesnt really help with mcbs rated at 6Ka

what are your thoughts as ive drawn a blank...?

the pfc just seems too high, its a new (to me) meter, with calibration cert done in jan

thanks for any help
 
Last edited:
In another thread on the same subject I pointed out that the OCPDs themselves can have significant impedances at the kA fault level (current limiting), as well as the relatively smaller size conductors on the outgoing ways, for instance what are the chances of say obtaining 16kA fault current levels at the outgoing way of a 6A breaker connected via a 1mm conductor ?, the further away from the origin you get the PFC rapidly diminishes. A small rise in impedance (both outgoing conductor and OCPD impedance) has a much larger corresponding effect on the PFC.

BS7671 even has a provision for this, as it does say this in parts further down in 435.1, "it may be assumed that the requirements of this section are satisfied as regards fault protection of the conductors on the load side of that point."

I read this (the bottom of paragraph of 435.1) to mean if there are doubts in respect of PFC levels that a further PFC measurement at the load side of that OCPD may well confirm that the OCPD is suitable, or not as the case may be., there are of course other exemptions, such as the 3m rule, annexe Za etc.
 

Reply to high pfc domestic property in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top