Hold on you said you did a PFC between Live and Neutral??? PFC is between Live and Earth You have measured a PSC which will be different on a TN S system. try it again on between Phase and Earth

Hang on chaps, we seem to be suffering from a difference in terminology.

PSCC = L-N fault current measurement
PEFC - L-E fault current measurement
PFC - is the highest of the two above readings noted on the test cert.
 
Hold on you said you did a PFC between Live and Neutral??? PFC is between Live and Earth You have measured a PSC which will be different on a TN S system. try it again on between Phase and Earth

The maxium prospective fault current is the current that would flow in the event of a fault either between live & earth (maxium prospective earth fault currrent) or between live conductors (maximum prospective short circuit current), whichever is the greater.
 
Had a quick look today, the L-N loop is .02 ohms, the supply voltage is 250v (another issue)

Andy,

You will measure 250v as this is the open circuit voltage across the sub-station windings esp as it sounds like you are sitting on the transformer! lol
It may be worth phoning the manufacturer of the CU; if they build to BSEN 60439-3 then this makes allowance up to 16k using 10k mcb's ~ speak to their tech dept. Remember IEE regs defer to manufacturers instructions.

I hope this is useful ;0)
Gaz.
 

Reply to High PFC in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
499
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
973
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

You cant just "avoid" the use of RCD's for nuisance tripping... it will depend on how the cable is routed. (ie buried less than 50mm) What has...
Replies
7
Views
476
Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
320

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top