Following on from another thread, I thought I would post up the results of my ZE and PFC.
I think the PFC results are high:

TNS
ZE is 0.7ohms
PFC (L to N) is 6.5ka and (L + E) is 4.4ka.

Would you fit 10ka breakers?

 
With those results you must be getting an amazing earth from your incoming service because your Ze would need to be about 20 times lower to get those values of PFC. 10m from the substation could cause those values though.
However if your PFC is >6kA then 10kA breakers would be required if the exemption for domestic consumer units protected by a BS1361 (i think) fuse being considered to have a breaking capacity of 16kA is not applicable.
 
For domestic you'll be fine.
As a bit of homework have a read of 434.5.1.

This permits devices to be protected against fault current by an upstream device; with limited A2s let through energy.
This is the case with circuit breakers and BS 1361 fuses where the fault current does not exceed 16kA.
Conditional ratings apply to the distribution board and its main switch and again usually relate to the protection being provided by a BS 1361 device and fault current upto 16kA

You must be close to the sub station then?
 
Your measurements are suspicious, it would appear either your Ze, or PEFC and PSSC are adrift by a factor of 10 high relative to each other. You would need some very good parallel earth paths (eg.structural steel) to get this sort of disparity in measurements.
 
What can be done?
Really It should be approx: 328amps using the formula 230/0.07.

I'm about 3 houses away from the supply transformer "with the Danger of Death" signs on it!

I'm gonna change the megger batteries tomorrow as well just in case its a erroneous reading
 
Last edited by a moderator:

Reply to High PFC in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
437
Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
2
Replies
22
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top