Hi All.

I had a job which was going to be a 'quicky' fault finding and repairing a couple of sockets, then it came to the testing.....

The consumer unit gave me no cause for alarm but was all labelled up wrong, so it turned out there were far more sockets and square meterage on this ring final than I first thought.

So I get, on end to end continuity (2.5/1.5 T&E)
r1=1.41 ohms, rn=1.43 ohms, r2=2.38 ohms. Then from that fig 8 test a range of R1+R2 from 1.53 to 2.61 ohms.

Way too high. Nulled the leads (again). Checked again...

If it was just one of those end to end readings that was too high, I would set about looking for a high resistance connection, but as the r1 is so similar to rn and the r2 is about right too - it seems unlikely that there is a high resistance joint in all three?

If I reverse input those readings to get a estimated cable length it comes out at around 190 metres!

The house is not particularly old - about 10 years I think. The floor area of the circuit is round about the 100 square metre mark, maybe more, and includes ground floor and first floor rooms - so the cable length could well be pretty high. On the limits at guess - but not way over as I have found.

Splitting this all down would be no easy task, and I've been told the wiring was 'inspected' three years ago during a change of ownership. So I'm looking to avoid the disruption, if possible. If anyone has any advice or ideas I'd certainly appreciate it - big time.

Are there any factors which might have given me misleading high readings?
 
Max Zs is 1.29 ohms on a B32. Correct for temperature I usually work to 1.10. So no - disconnection times not met.

Mountain out of a mole hill? I thought disconnection times were there for a reason - I mean how do I write it up. Is it not in -unsafe condition?
 
I assume it's on an RCD? Bs 7671 permits an RCD to take care of earth fault protection on a TN system, in which case your max Zs becomes 1667 ohms. I'm not saying that would be usual practice, but this is a circuit only marginally over required criteria. I just cant see the point in major disruption and expense for a circuit like this. Alternatively loadings permitting, stick it on a 20a OCPD
 
Max Zs is 1.29 ohms on a B32. Correct for temperature I usually work to 1.10. So no - disconnection times not met.

Mountain out of a mole hill? I thought disconnection times were there for a reason - I mean how do I write it up. Is it not in -unsafe condition?
I assume it's on an RCD? Bs 7671 permits an RCD to take care of earth fault protection on a TN system, in which case your max Zs becomes 1667 ohms. I'm not saying that would be usual practice, but this is a circuit only marginally over required criteria. I just cant see the point in major disruption and expense for a circuit like this. Alternatively loadings permitting, stick it on a 20a OCPD[/QUOTE
 
It's up to you to determine whether it's safe, your name on the form, I'm just saying what I'd do. Regarding the 30/32a device for a ring final, if you feel the load is OK for a 20a then put it on the form as a departure and justify it with the reason you've given that it is a poorly designed circuit and reducing the OCPD rating is making it safer.
Personally I'd list the high circuit readings on the form with explanation, leave it on a 32a and state that the RCD is meeting disconnection times and that I consider the circuit poorly designed but safe for continued use.
 

Reply to High r1, rn, r2 etc on ring final. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top