High R2 - Lighting Circuit | Page 3 | on ElectriciansForums
Discuss High R2 - Lighting Circuit in the UK Electrical Forum area at ElectriciansForums.net
Sheffield
Hi all,
I was hoping to sneak in a little job late this afternoon - changing a faulty bathroom pull chord for an outside switch plate. No problems with access. Straight forward enough.
House is almost certainly post 60's. CPC's present in lighting circuit.
Live Zs = open circuit.
R2 test with wander lead from MET to as many lighting JB's in the loft I could find = 60 k ohms.
So there is some sort of reading.
Loose connection?
Back tomorrow so any advice on where to start always appreciated.
It looks like the lights are wired in single line + cpc, looped in an out using every which method you can think of, and a neutral looping around each load.
Like I said - where to start.
There are other circuits available in the loft - I could bridge across from 1 JB to another with some 4.0mm if I have to (I suppose).
[ElectriciansForums.net] High R2 - Lighting Circuit
now that came to mind !
Thanks All. Sure enough CPC was present at consumer unit in with the line. It reached two out of the 8 rooms in the circuit.
Found no less than 4 disconnect CPC’s at junction boxes. I managed to clear the faults to switches at least and a couple of pendants. Never got round to the downlighters - that’s a can if worms. Pretty sure all the CPC faults were caused by whoever riddled the ceiling with the downlighters. Very poor installation.
The customer grumbled about the fault finding though stated ‘I want everything safe for insurance purposes’ but wasn’t prepared to pay for it. I basically worked for an extra 3 hours for free.
Perhaps if the fault was on the line or neutral they would be more understanding?
Thanks all. I can close this ‘Minor Works’ out.
I had a issue with the RCD testing though - all three failed.....new thread.
Reply to High R2 - Lighting Circuit in the UK Electrical Forum area at ElectriciansForums.net
Ok I’ll try this when I’m down
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...