Hi all,
I was hoping to sneak in a little job late this afternoon - changing a faulty bathroom pull chord for an outside switch plate. No problems with access. Straight forward enough.
House is almost certainly post 60's. CPC's present in lighting circuit.
Live Zs = open circuit.
R2 test with wander lead from MET to as many lighting JB's in the loft I could find = 60 k ohms.
So there is some sort of reading.
Loose connection?
Back tomorrow so any advice on where to start always appreciated.
It looks like the lights are wired in single line + cpc, looped in an out using every which method you can think of, and a neutral looping around each load.
Like I said - where to start.
There are other circuits available in the loft - I could bridge across from 1 JB to another with some 4.0mm if I have to (I suppose).
The customer grumbled about the fault finding though stated ‘I want everything safe for insurance purposes’ but wasn’t prepared to pay for it. I basically worked for an extra 3 hours for free.
I would have walked away from that job. before I start a job I tell the customer
if you want a job doing I tell them no earths on lighting circuits, right down to the bonding the job will not be done .
View attachment 40297now that came to mind !
I think I must be a soft touch. I take a conscientious approach and always do loads of little extras ‘I’ll just tidy that up so they have no further problems’
I need to toughen up.
I’m a . (Supposed to be a -----!)
Today was a school day in so many ways.
Reply to High R2 - Lighting Circuit in the UK Electrical Forum area at ElectriciansForums.net
Ok I’ll try this when I’m down
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...