Think it's hard to justify a code 2 (potentially dangerous) if the install is protected by at least one functional 30 ma RCD which we know will provide protection in accordance with BS 7671 up to 1667 ohms.....After all bringing it down to <200 ohms as recommended in Bs 7671 will make no difference to the safety of the protection as it stands. Code 3 for me.
This is not intended to start another Ra 'debate' with E54....but an EICR is based on Bs7671 whether E54 or anyone else agrees or not,and coding should be based on that alone,not personal views on Ra values.

And i agree with you, ....to a point!! ..lol!!

There are most certainly times, due to very unfavorable ground conditions where your not going to even achieve the numbty BS 7671 200 ohms Ra. But i think you'll agree that in such circumstances it's sensible to add an up-front S type RCD, rather than totally relying on a single RCD device!!?

Mind, there are some members that blindly believe that all or single RCD devices can always be relied on, because they virtually never fail!! Well, that's what they have read anyway!!
 
And i agree with you, ....to a point!! ..lol!!

There are most certainly times, due to very unfavorable ground conditions where your not going to even achieve the numbty BS 7671 200 ohms Ra. But i think you'll agree that in such circumstances it's sensible to add an up-front S type RCD, rather than totally relying on a single RCD device!!?

Mind, there are some members that blindly believe that all or single RCD devices can always be relied on, because they virtually never fail!! Well, that's what they have read anyway!!


Agree with upfront S type....but the point I was making was for the purposes of an EICR ( which is the OP's query) the only consideration is compliance with Bs 7671....it is not the done thing to introduce personal preferences into coding of defects.
 
Last edited by a moderator:
Hi guys, I would like to know what code you would give for a reading of 435 ohms on an EICR. Personally I'd give a C2.

Regards

411.5.3 Note 2 merely states that anything over 200 ohms MAY not be stable. So, is your 435 ohms a stable reading? Has there been previous tests of the Ra for you to compare it with? What other protection does the installation have?

I don't think you can just say because the Ra is 435 ohms it is unstable/too high?

I've got some good Ra readings recently on new installs - give a burley customer 4 rods, connectors, a sledge hammer and the knowledge that if I don't have to install the rods he saves money; then all he only sees is a challenge - less than 40 ohms :)
 
411.5.3 Note 2 merely states that anything over 200 ohms MAY not be stable. So, is your 435 ohms a stable reading? Has there been previous tests of the Ra for you to compare it with? What other protection does the installation have?

I don't think you can just say because the Ra is 435 ohms it is unstable/too high?

I've got some good Ra readings recently on new installs - give a burley customer 4 rods, connectors, a sledge hammer and the knowledge that if I don't have to install the rods he saves money; then all he only sees is a challenge - less than 40 ohms :)

So let the customer sink the electrodes with the understanding that if he/she breaks any drains then it's their fault.... I like your style :)
 
411.5.3 Note 2 merely states that anything over 200 ohms MAY not be stable. So, is your 435 ohms a stable reading? Has there been previous tests of the Ra for you to compare it with? What other protection does the installation have?

I don't think you can just say because the Ra is 435 ohms it is unstable/too high?

I've got some good Ra readings recently on new installs - give a burley customer 4 rods, connectors, a sledge hammer and the knowledge that if I don't have to install the rods he saves money; then all he only sees is a challenge - less than 40 ohms :)


435 ohms? in the event of an earth fault your overcurrent device wont operate,your RCD will.
40 ohms? in the event of an earth fault your overcurrent device wont operate,your RCD will.

Yep,can see the real advantage of getting 40 ohms.:rolleyes2:
 
435 ohms? in the event of an earth fault your overcurrent device wont operate,your RCD will.
40 ohms? in the event of an earth fault your overcurrent device wont operate,your RCD will.

Yep,can see the real advantage of getting 40 ohms.:rolleyes2:

Here we go again!! lol!! Anyone with an once of commonsense would be far happier with a stable deep driven 40 ohm Ra, than your all singing, all dancing but useless single twig 200 ohm Ra, that will never become stable!!
As this example is made up of 4 coupled rods, the chances are that the final Ra will be substantially lower, after the soil has consolidated/compacted around the top 3 rods...

Seems your reverting back to relying on a single RCD device for a TT system again here too!! lol!!
 
Cheers E54.
I nearly went back today and ripped the whole lot out so I could stick a banana in the ground, hoping the potassium would give me a better reading :)
 
Cheers E54.
I nearly went back today and ripped the whole lot out so I could stick a banana in the ground, hoping the potassium would give me a better reading :)

No problem ...lol!! The whole idea here, should be to encourage electricians to do there best within reason, to get the best Ra value they can by applying a little thought in what they are doing!! Not encouraging people to just bung a twig in the ground and hope for the best, mainly because it's never gonna happen.
 
No problem ...lol!! The whole idea here, should be to encourage electricians to do there best within reason, to get the best Ra value they can by applying a little thought in what they are doing!! Not encouraging people to just bung a twig in the ground and hope for the best, mainly because it's never gonna happen.

If you get a TN value which will operate an overcurrent device then I salute you,the end result was worth the effort....if you think 40 ohms is any better than 100 ohms or 200 ohms you are kidding yourself.....
 
Yeah, those Screw fix (et al) twigs are a joke.
To be honest I was happy with 40ish ohms because when put into context, when I've PIR'd plenty of Nationally owned campsites I've measured far, far worse readings
 

Reply to High TT Ze!Personally in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

Similar threads

It was purely an off the top of my head example, but I'd say - accessible live parts C1 - inaccessible live parts C2 - 10 feet up in a locked room...
Replies
9
Views
719
Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
2
Replies
22
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top