Only Sometimes? Lucky you!sometimes electrics is a crap job, innit?
Think it's hard to justify a code 2 (potentially dangerous) if the install is protected by at least one functional 30 ma RCD which we know will provide protection in accordance with BS 7671 up to 1667 ohms.....After all bringing it down to <200 ohms as recommended in Bs 7671 will make no difference to the safety of the protection as it stands. Code 3 for me.
This is not intended to start another Ra 'debate' with E54....but an EICR is based on Bs7671 whether E54 or anyone else agrees or not,and coding should be based on that alone,not personal views on Ra values.
And i agree with you, ....to a point!! ..lol!!
There are most certainly times, due to very unfavorable ground conditions where your not going to even achieve the numbty BS 7671 200 ohms Ra. But i think you'll agree that in such circumstances it's sensible to add an up-front S type RCD, rather than totally relying on a single RCD device!!?
Mind, there are some members that blindly believe that all or single RCD devices can always be relied on, because they virtually never fail!! Well, that's what they have read anyway!!
Hi guys, I would like to know what code you would give for a reading of 435 ohms on an EICR. Personally I'd give a C2.
Regards
411.5.3 Note 2 merely states that anything over 200 ohms MAY not be stable. So, is your 435 ohms a stable reading? Has there been previous tests of the Ra for you to compare it with? What other protection does the installation have?
I don't think you can just say because the Ra is 435 ohms it is unstable/too high?
I've got some good Ra readings recently on new installs - give a burley customer 4 rods, connectors, a sledge hammer and the knowledge that if I don't have to install the rods he saves money; then all he only sees is a challenge - less than 40 ohms
An apprentice, what else would you use
411.5.3 Note 2 merely states that anything over 200 ohms MAY not be stable. So, is your 435 ohms a stable reading? Has there been previous tests of the Ra for you to compare it with? What other protection does the installation have?
I don't think you can just say because the Ra is 435 ohms it is unstable/too high?
I've got some good Ra readings recently on new installs - give a burley customer 4 rods, connectors, a sledge hammer and the knowledge that if I don't have to install the rods he saves money; then all he only sees is a challenge - less than 40 ohms
435 ohms? in the event of an earth fault your overcurrent device wont operate,your RCD will.
40 ohms? in the event of an earth fault your overcurrent device wont operate,your RCD will.
Yep,can see the real advantage of getting 40 ohms.:rolleyes2:
Cheers E54.
I nearly went back today and ripped the whole lot out so I could stick a banana in the ground, hoping the potassium would give me a better reading
No problem ...lol!! The whole idea here, should be to encourage electricians to do there best within reason, to get the best Ra value they can by applying a little thought in what they are doing!! Not encouraging people to just bung a twig in the ground and hope for the best, mainly because it's never gonna happen.