Morning chaps,

A bit of background. Finished a job yesterday, it was a bathroom install for the council on a private job. So with these they are grant work for the disabled, existing installtion dated, we have to note this on the certificate and install new circuit off a small new board for our installation. Earthing and Bonding ok etc etc. My installation all Fine and conplies with the regs.

Before starting noted it was a TN-S system, phoned up told it was an 80A fuse etc etc.

Came to test the Ze, PFC, initial IRs at the end of the first fix. Open up the dated unsealed DNO head. Found a fused neutral, Ze reading of 6.63 Ohms. Phoned the DNO, within a hour someone had come and put a front end RCD on the whole installation then 2 Hours after that they were under next doors floor repairing the cable, new head fitted top job. New Ze of 0.24 Ohms.

Now, this house had had a hob fitted on a new circuit by a local NIC electrician 6 months ago, got hold of the certificate and he had got high Ze readings aswell. I asked the owner (90 year old lady) and she didnt know anything, however her daughter said the electrician told them there was a high reading they needed to sort, but gave them no contact details, info or anything. He left the house knowing the 3036 fuses in her main board (2 of which had 1.5 in them instead of fuse wire, which i replaced, when doing these grant jobs i alway make sure the existing fuse wires are atleast fused correctly) would not be under their maximum Zs readings(No RCD).

Which brings the question, i have always notified the DNO on behalf of the customer for anything not fit... Is it our responsibility or the owner of the house?

Cheers
 
op said that fuse was unsealed. all very well to call DNO to come out and check, but who pays for my time waiting for them ? can't tell customer that they will be out in 5 hours, so i'll be charging ÂŁ25/hour to sit there doing nowt.
 

Reply to High Ze, Whose. Responsibility. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
2
Replies
22
Views
1K
  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top