Had the DNO out last week to remove old three phase overhead lines to a property undergoing refurbishment as they were sagging really low (within 2m from the ground!), had been for years and the new owner didn't like the look of them! Anyway the DNO agreed to remove and joint a new underground supply from the existing pole to a new location at the other end of the property. After all the work was done they mentioned that they dropped the fuses from 80A to 60A due to high EFLI.
Firm I work for only have Metrel MFTs, can't remember model off top of my head but all the same model. Went to test the new board before energising and I'm getting a Ze of 0.44... on a TN-C-S. Now these MFTs can only do no trip, and I'm aware of that higher readings no trip can give but the only way of getting a lower reading is to reduce the test current. Reducing to 30ma for example gives 0.34, even that's not ideal! I feel uncomfortable with these readings but we don't have a high current tester.
So... should I push for a new tester to verify the reading or just recommend getting the DNO out?
Nothing wrong with that 0.44 Ze figure, especially now the DNO have reduced the fuse rating. Oh and the chances are, that being an overhead supply, this will in fact be a full PME system. Just too many consumers being fed from it, plus you may be at, or close to the end of a very long line of poles after the supply TX....
If it's a 61557, which it probably is, they can of course do a high current loop test. They are as Trev says a damn good piece of kit.
I know you can push the no trip test current up to 1A, but that's still under no trip.
It's on an ex farm, you can see the poles working their way up the hill ending at this property not going anywhere else or branching off. I bet it's at the end as you say.
Cheers for the assistance all!
Reply to High Ze... in the UK Electrical Forum area at ElectriciansForums.net
Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!