T

timo

Just extended a ring to include 4 more sockets.

Arangement =T-N-C-S
ZE of .27 and R1 + R2 of the ring is .67 ohms max

So by calc Zs should be .94 ohms. Im getting 1.3 ohms on zs test at sockets. anything from 0.7 to 1.3 ohms around the ring.

:confused:
 
Are you getting the higher readings on old sockets or new or both ?

The ones with the higher readings may be wear and tear issues or poor connections generally.

May be beneficial to remove the socket plate and test off the bare conductor ends alone, to rule out the socket plate itself. !

I'm assuming your are using a "socket and see" type adapter at the socket with your meter ? Do the readings change if you wiggle it in the socket ?
 
Thanks for the reply GT. The readings are on both old and new. The sockets were re-wired when the house was done up a few years ago i think. (all brown and blue) the existing is the same, some are .7 and some are 1.1 to 1.3. The new ones are 1.3 to all.

If there was a lose socket from etc wouldnt the R1 + R2 get this ? all the readings from the R1+R2 and L-N crossed on test were fine and max was .67 ohms and all within .05 ohms of each other.
 
Have you got an RCD on the board? Sometimes they can put anything up to half an ohm on the circuit. If so, measure the impedance both sides of the RCD at the board and see if you get a difference. Also, if you've got a non trip loop test, they can sometimes give spurious ( :) )readings due to the low currents used....
 
I would also double check that they are all on the ring, with those readings it sounds as if there may be a spur there as well.
 
thanks for the heads up on the RCD and Testers. And YES to both. 30MA on sockets and my tester is the easitest with the Trip Lock function thats allows me to check when RCDs in circuit.

The sockets with high readings are part of the ring and not spurs :( checked that one too
 
Last edited by a moderator:
Sorry I had not read the previous thread.
I have a metrel easitest and do not trust it on trip lock zs readings
You are allowed to add your measured Ze to the R1+R2 established on the cold ring checks checks...see IEE guidance notes. Inspection and testing,
Greeny
 
Just to eliminate a problem with your tester lead or the actual socket change the lead on the tester to the 3 lead kit then unscrew the socket and test it at the terminals me thinks you will find you may get a differant reading .
 
Just to eliminate a problem with your tester lead or the actual socket change the lead on the tester to the 3 lead kit then unscrew the socket and test it at the terminals me thinks you will find you may get a differant reading .

Will try this one. Thanks
 
personally id do an r1 + r2 at all the sockets on the 'ring', think you may get a suprise

The OP actually said that he's already done that in the first post, and reiterated that a few posts later, including cross connection of line and neutral too.

It sounds like he knows how to test a ring.
 

Reply to High ZS but R1+R2 and Ze ok in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
996
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top