Nice thread, took a long time to get an answer for swapping for type b though . MG have never made a C60H type B rcbo dunno why ,
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss High Zs on cct in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
No, sorrry
Everything you are saying makes sense, but it still doesn't explain why it drops in that one column only.
Let's take our formula:
Ra x I delta n = 50v .....This is one of the requirements that have to be met if RCD used for earth fault protection.
so...
Ra = 50/I delta n
For a 30mA RCD
Ra = 50/.03 = 1667 ohms
Now the figures used above remain constant throughout the 4 columns in table 41.5
i.e. touch voltage 50v, current 30mA .........coz that's the equation they have to satisfy
the only thing that changes is the resistance figure in column 3
Because the touch voltage theoretically will be 250V (5 x 50V) which exceeds 230V but not 400V.
But as we dont have a 250V voltage the sum is calculated using our 230V which gives us the resistance of 1533ohms.
51v to120v...............1667
121v to 230v..............1667
231v to 400v..............1533
401v & higher.............1667
So why, at this nominal voltage, does it alter?
Why does it alter back again in the next column?
And there is one more question I'd like to ask.
As our regs don't cover supply distribution, where are we likely to encounter Uo bigger than 230v (like column 3 & 4 refer to)?
Would this be on private supply systems, as opposed to public?
Obviously there is an allowance for our supply voltage as it is never bang on 230V hence the allowed tolerances.
I'm sorry if I'm getting annoying with this now, but I'm one of those irritating b""""""s who won't let something go until I understand it
No annoying at all mate.....I like a challenge.
Nice thread, took a long time to get an answer for swapping for type b though . MG have never made a C60H type B rcbo dunno why ,
my 1st post on page 1 mentioned this and also the chance of contacting the manufacturer to see if he would allow a higher zs
the thread just went a little off piste
The circuit is protected by an rcbo.....the max Zs for the mcb part of the rcbo is rendered irrelevant by the rcd part of the rcbo which will ensure the disconnection time is achieved at a Zs of up to 1667 ohms.
Of course the zs is relevant....but any problems with a very high zs on a TN system should be picked up and rectified before the zs is even measured...high ze or R1R2 for instance.
In the case discussed here the measured zs is only a tiny fraction of an ohm above the max zs for the mcb to meet the required disconnection time.If the mcb was the only means of meeting the disconnection time it would need to be changed,but in this instance the rcd element of the rcbo ensures the disconnection time will be met up to a zs of 1667 ohms.
For the life of me I cannot see the logic of changing the mcb type to achieve a disconnection time which is already met by the existing protective device.
If it was a TT system, then I would be attempting to get all readings below 100 ohms no matter what the front end RCD is. If it was a TN system, then I would completely disregard all maximum Zs's relating to RCD's and just work to the max Zs's from MCB's as you would.