High Zs on cct | Page 4 | on ElectriciansForums
Discuss High Zs on cct in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
If it's a decent TN-S system, why are the Zs so high? 80 ohms is a ridiculous value for this type of system, and if common sense prevails then investigative works should be put into action to find out why it's so high with a TN type supply.
on that supply the Ze was .35 ohms, so it was ok.
what we are up against is the engineer thinks everything is ok if it's below 1667 ohms.
yes i think we definitely need to investigate the 80 ohms measured circuits and other like that, but the engineer will not put labour on it, just passes them.
by the way the circuits are for temporary supplies and the main distribution supplies with the RCDs are only fully tested every 12 months and functional tested every 3 months. I think they should be fully tested every 3 months.
i wasn't testing that cable myself, it was a 3 phase cable, one of the phases had the high 80 ohms. cable size is 4mm and long runs, type is SY, perhaps 100 mtrs to a distribution board. Zs from the distribution board ok at something similar to .35 ohms. then another 125 mtr run in 125mm cable to the supply. Ze .35 ohms at the supply
So only one phase on a three phase supply has a high Zs reading, and the other 2 are okay?
the others have readings of 4 ohms, which is about the max of approx 2 ohms in the Regs for MCBs on the TN-S system.
so they would fail if you went by the regs.
but the engineer is saying that anything below 1500 ohms approx passes.
I am working on a very large site in England. The engineers are saying it doesn't come under the IEE regs, but obviously it does come under the health ad safety at work act.
The supply is TN-S with permanent distribution units with RCDs. They supply temporary leads, lighting power etc.
I'm sorry, but from what I can make out form your querey.......your engineer chappy is a plank!
You state you have a Ze of 0.35 on a TN-S system and a further Zdb of around the same, yet some of the circuits are measuring out at 80 ohms!!!!!!
Does he have any idea how long a circuit would have to be to return a Zs reading that high with that associated Zdb???
But it's ok because theres an RCD on the circuit.....I've never heard such horse **** in all my life. There is obviously a serious issue there somewhere, one that needs addressing ASAP.
Ok just to satisfy my curiosity I've done a rough calc and in order to obtain a Zs of 80 ohms without any circuit faults for a 4mm+4mm SY cable and your Zdb of 0.35ish as you say, the length of run would have to be around 230M. Does this sound right as a length of run to you???
The only thing that springs to mind is that the engineer was aware of this but rather than sort out what is obviously a problem he took the easy way out and gave additional protection via a 30mA RCD. A cop out in my book in this instance.
But that's only for one phase, the other two are 4 ohms! I suspect a high resistance joint or damaged cable myself.
I think we've had this discussion a few times before too, bad circuit design for the 4 ohm bit, and a bit of ooh b*gger, I had better stick an RCD on that.
Poor work indeed.
Thats the point I was making.....for the other 2 to be 4ohms and 1 @ 80ohms, obviously an issue there somewhere as no-one in their right mind would install a 4mm radial @ 230M.:)
Poor work indeed.
An engineer indeed:rolleyes:
Some of the temporary leads etc maybe 230 mtrs long , due to other trades plugging in extension leads upon extension leads. But on the circuit mentioned it was 'designed' to be that long.
He is also quoting a max volt drop of 6% on lighting (not 3% as in the regs) from local MV supply.
Yes all these bad reading should be investigated, but i think the engineer (apart from not knowing what he's doing) doesn't have enough labour to assign to those tasks. small budget, very large site.
The RCDs are permanently fitted to the main permanent distribution units.
At the end of the day, no matter how long a circuit was all 3 phases should have a Zs almost identical to one another....give or take a 0.01-2.
For one 2 to be @ 4ohms and 1 to be @ 80ohms, even my Nan would investigate that!!!!
yes probably a cop out.
all the sparks on the section are not happy with it. they are all praying no accidents will happen.
Reply to High Zs on cct in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...