High zs on RCD's. | on ElectriciansForums

Discuss High zs on RCD's. in the Talk Electrician area at ElectriciansForums.net

dlt27

-
Joined
Jul 4, 2011
Messages
196
Reaction score
30
Hi all. I carried out an EICR yesterday. It was a BG split load consumer unit and when testing I noticed the zs values were coming out high.
I noticed on the 1 rcd there was 0.50 Ohms difference between feed and load side of rcd and on rcd 2 there was 0.60 Ohms difference. Just wondered if anybody else had found this and also does anybody think it needs further investigation. I know the zs doesn't really matter because the rcd Will still trip at 1667 ohms. However just wondered what everybody else thought because I've never come across it before. Thanks
 
Exactly as Spin has stated, bridge them out if your that worried. So long as the RCD's test out correctly on RCD testing, you shouldn't have anything to worry about....
 
Very rarely come across an RCD protected circuit with a true loop impedance reading. Agreement with the above comments.
 
Rcd's love to add impedance to true Zs values that in reality don't really exist.
Remember your tester is an electronic device just like the Rcd's.
There like a married couple always contradicting each other.
The tester has a no trip function, the Rcd contributes to this with capacitance back emf's and all those other thingy ma gigs.
If extreme, it may even throw up a noisy circuit fault code on yer tester.
Take it out of circuit and replace with an mcb for test purposes and take a true Zs value and you will see a difference.
That with your R1/R2 reading and tripp times will confirm compliance.
 
Hi all. I carried out an EICR yesterday. It was a BG split load consumer unit and when testing I noticed the zs values were coming out high.
I noticed on the 1 rcd there was 0.50 Ohms difference between feed and load side of rcd and on rcd 2 there was 0.60 Ohms difference. Just wondered if anybody else had found this and also does anybody think it needs further investigation. I know the zs doesn't really matter because the rcd Will still trip at 1667 ohms. However just wondered what everybody else thought because I've never come across it before. Thanks

I often note the impedance that has been added by RCD on my EIC / MW and always do if it takes the Zs beyond maximum satisfactory disconnection by MCB protected by it.
 
Some manufacturers' earth fault loop impedance testers ("MFTs") are more susceptible to this than others. Some call it "RCD uplift". It can be up to an ohm in some cases.
 
to go to the extreme, i had BG comdemn an installation as he read out of limit Zs. my 1553 confirmed a Zs at sockets of 351 ohms. testing across L busbar and E in the CU gave 349 ohms. Ze on the upfront RCD incoming L and E was 0.2 ohms.
 

Reply to High zs on RCD's. in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
783
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

  • Question
Yea all out circuits were disconnected & Rcd ramped tested Think this will be the right way forward,with EL clamp meter Cheers have a nice Christmas 😎
Replies
2
Views
1K
I fitted a Mem MR30 Pod and MCB, about £75 for both.
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top