Hi chaps.
On some remedial works at a school, I have a sub main a 16mm armoured feeding it about 50m away from the main DB. Fed from a C63 triple pole 60898.
The issue I have is the Zs at this submain is 0.46 which is way over the maximum permitted.
But the Ze at the main DB is 0.35. On a tncs btw, which I feel maybe too high also.
How can we bring this down? Or can this be noted down on the test sheets that the Ze is high hence the high Zs reading?
Thanks