Holy thread bump batman etc.
How did you resolve this? Any new ideas?
Had a CU on a submain reading 0.29 - made compliant by using an 80a fuse at the origin, but not wholly satisfied as this could be swapped out, and while unlikely to ever give issue probably doesn't meet the max demand (silly as it is.)
Origin was 0.28 (TNS) and submain was a few meters of 25mm SWA
Looking for inspiration as the DNO in these parts is fairly hostile towards enquiries on safety or maintenance of their largely interwar network, and given its crumbling state it's a problem I expect to encounter again.
Single RCD protecting submain and therefore whole house is not ideal.
Two submains/CUs on 60amp? Seems lunacy but it works.
However BS7671 states its zs figures are worst case scenarios and that manufactures may offer devices compliant with higher values... Anyone researched who/what?
And finally.... How is it that my submain reading .29 would not comply but the 100 amp fuse at the origin is quite alright for anything up to 0.8 then?