True, but it should always designed for the worse case scenario as the DNO will probably just say well its within our acceptable limits.I agree it has been badly designed. That said the Ze may not have always been 0.35.
In this scenario you have two options.
1. To encase the complete cable run in material that will contain any fire risk that may occur from the OCPD not tripping in time.
2. To install RCD protection to the cable as RCDs have far higher maximum permitted Zs values.
The first option is not really an option due to cost so this only leaves the second option. A 500mA RCD has a max permitted Zs of 100 ohms so I would advise installing one of these at the supply end of the cable.
If you are doing an EICR I would code it as a C2 if there is currently no RCD protection on the cable.
Funnily enough it is in metal trunk all the way to the DB.
Think I’ll speak to my QS about the RCD option.
Many thanks for the advice.
Yeah, it was picked up on an eicr we done last year. It’s just everything has been done to lower the values but to no prevail.
Out of interest what have you done to lower the values to lower than the Ze?
Unfortunately yes.Does it need to be 63A.
Just what I can reasonably do practically, tightened all connections, contact cleaner, supplementary bonding.
Hi - with B63 the max goes up from 0.35 to 0.69 and job's done (?).