Can you not put the Main Tails into Henley blocks and install a 60A Fused Switch as previously stated.

I understand some schools this will not be possible due to the cables coming from an outside substation into a panel board. However with your Ze of 0.35 I would assume the school is not large enough for its own transformer and sub.
 
Have you measured Zn to ensure that your OCPD will disconnect in short circuit conditions?

If good then I would add an RCD as previously mentioned, I'm not a fan of using RCDs for fault protection however you've been left with a poorly designed installation that you need to rectify at limited cost.

Also I would opt for fuses rather than MCB to give you a little more scope for supply variances etc.
 
Have you measured Zn to ensure that your OCPD will disconnect in short circuit conditions?
That was my thought, if it's tncs then if the pscc is higher than the pefc at the cutout then there is an issue for the dno to resolve, as you'd be measuring the same cable through two different terminals.
However in its favour the fact that the cable is armoured could make short circuit less likely without an earth fault, so overload protection is more important
 
Whatever is the solution time is running out they are back to school in a week! Have you got no access to the O&M manual/test certificates? as if it complied when installed.
 
Holy thread bump batman etc.

How did you resolve this? Any new ideas?

Had a CU on a submain reading 0.29 - made compliant by using an 80a fuse at the origin, but not wholly satisfied as this could be swapped out, and while unlikely to ever give issue probably doesn't meet the max demand (silly as it is.)

Origin was 0.28 (TNS) and submain was a few meters of 25mm SWA

Looking for inspiration as the DNO in these parts is fairly hostile towards enquiries on safety or maintenance of their largely interwar network, and given its crumbling state it's a problem I expect to encounter again.

Single RCD protecting submain and therefore whole house is not ideal.

Two submains/CUs on 60amp? Seems lunacy but it works.

However BS7671 states its zs figures are worst case scenarios and that manufactures may offer devices compliant with higher values... Anyone researched who/what?

And finally.... How is it that my submain reading .29 would not comply but the 100 amp fuse at the origin is quite alright for anything up to 0.8 then?
 
Single RCD protecting submain and therefore whole house is not ideal.
If it is 100mA/300mA delay RCD feeding the sub-main and the house CU is all on RCD (or neutral-switching RCBOs like compact Wylex/Fusebox) then you keep final circuit selectivity and avoid marginal Zs limits.

Not a substitute for anything very suspect in the way of supply Ze, but if the system is otherwise sound but just not up to meeting 5s disconnect on the sub-main fuse then it is a valid approach and ticks all of the regulations.
 
And finally.... How is it that my submain reading .29 would not comply but the 100 amp fuse at the origin is quite alright for anything up to 0.8 then?
The DNO fuse is for overload protection of their network, it is not required to meet the BS7671 regulations on ADS for an installation.
 

Reply to High Zs on submains and high Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Question
It is a TNS system, the earth rod is providing an earth reference to make on epile of the supply neutral and is not part of the earth fault loop...
Replies
20
Views
4K
davesparks
D
OK that looks even better. That is one thing I hate about the Schneider (and other) MCCBs is the huge number of variants and the rubbish...
Replies
9
Views
2K
  • Question
Have you double checked your busbar connections to make sure you haven't accidentally got the finger behind the main switch terminal?
    • Like
Replies
11
Views
5K
15ohm is fine but i would be looking at why fault protection is not provided by the supply, something seems amiss with the earthing plus if the...
Replies
9
Views
2K
  • Question
Youre in the same boat as me. I was previously with niceic and later on, napit. No issues. I didn't bother finishing my nvq3 as in 2010 during the...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks