Hello,
looking for some advice on 2 things please.
Ive tested a ring main in a house with RCD protection, the results ive had are
L-L .43
N-N . 41
E-E 1.17
I had a look for a loose connection but can’t find anything, how high does the CPC reading need to be before you would consider it ‘to high’?
the second question is regarding the same circuit, they have a fuse spur fed from one of the sockets and then have 6 x double sockets after the fuse spur. The last 3 are out door and the last socket on the ‘radial’ gives a Zs reading of 1.64.
Am I right in saying max Zs should be 1.08? Is the high reading due to the distance on the run after the fuse spur?
Is the reading acceptable?
the reading on all sockets were lower than .71 until the last 3 outside which are run using SWA cable.
thanks
looking for some advice on 2 things please.
Ive tested a ring main in a house with RCD protection, the results ive had are
L-L .43
N-N . 41
E-E 1.17
I had a look for a loose connection but can’t find anything, how high does the CPC reading need to be before you would consider it ‘to high’?
the second question is regarding the same circuit, they have a fuse spur fed from one of the sockets and then have 6 x double sockets after the fuse spur. The last 3 are out door and the last socket on the ‘radial’ gives a Zs reading of 1.64.
Am I right in saying max Zs should be 1.08? Is the high reading due to the distance on the run after the fuse spur?
Is the reading acceptable?
the reading on all sockets were lower than .71 until the last 3 outside which are run using SWA cable.
thanks