Hi all, Doing some pre board change testing and ive found 2 sockets with high Zs readings. Everything else is fine, done all my end to ends and the Zs's are what should be expected. A couple of the sockets have Zs lower than expected but 2 are higher. They should be about 0.8 ohms but ive got one at 1.20 and one at 1.40. Taken the highest value socket off, re terminated, still high. Tested at the terminals of the socket just in case the socket was duff, but still high. Its a PME system with a good low ZE (0.15). Any thoughts people??
 
Im still scratching my head a bit as to why my r1 rn r2 values on the offending ring are as high as they are. The circuit cant be over 120m, so why so high?? ultimately if the Zs ok then its not a problem. Unfortunately my brain doesnt work like that and i always what to know why things are what they are!! Bit OCD!

Haha, you might get lucky and find 100m drum of 2.5 in the loft with the ends connected to make part of the ring main. Get digging!

On a serious note... are there any sheds or outbuilding you could have possibly missed where they have installed that as part of a ring main? I have seen that down before!
 
Haha, you might get lucky and find 100m drum of 2.5 in the loft with the ends connected to make part of the ring main. Get digging!

On a serious note... are there any sheds or outbuilding you could have possibly missed where they have installed that as part of a ring main? I have seen that down before!
I was just thinking that.... half a reel in the loft! No,nothing outside. The customer has asked me to put some outside sockets in for him. Better put them on their own circuit or the end to ends will be off the map!!
 
Mystery solved. Took a few socket covers off and found lots of loose/poor earth connections and loose live connections also. Sorted these out and got much better Zs values and lower end to end values at the board. I carried out end to end tests at the problem socket (as a few of you guys recommended) and got readings of 0.03 for r1 and rn.
 

Reply to High Zs value with 2 sockets in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
886
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
2
Replies
22
Views
1K
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top