History of PME Systems. | on ElectriciansForums

Discuss History of PME Systems. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Joined
May 31, 2009
Messages
579
Reaction score
240
Location
Surrey
Does anyone know the history or reasoning behind PME and TN-C-S earthing? It came up today and I thought it was worth knowing.

Why was it brought in and when?
 
Cheaper to install than running a separate earthing conductor along side the supply.
As for when, I don’t know late 70s perhaps?
 
But the old cables were lead sheath? They didn’t have a separate earth conductor. The lead would have added a cost though I suppose.

Is that the only reason? Just cost?

And what the danger of a lost N, why did they think this was safe?
 
Lost n will be discovered very fast. Lost e would not be. So it makes sense to combine as long as you trust your equipotential zone and bonding.
So you could say pme was a safety improvement, a bit like putting your smoke alarms on the lighting circuit.
Has anyone got figures for death by pme Vs death by tn-s?
 
And if the pipes are not bonded, appliances and everything metal that’s connected to a CPC becomes live. That’s not an improvement. But as you say, you’d need to trust your equipotential zone.
 
The lost Nuetral could go undetected forever though because of the bonding as long as the pipes that are bonded are actually extraneous
Would that not be obvious due to high resistance neutral?
And if the pipes are not bonded, appliances and everything metal that’s connected to a CPC becomes live.
as you trust your equipotential zone and bonding
Yes no bonding would be dangerous
 

Reply to History of PME Systems. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
918
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
To give you some idea....with my DNO, the question "Can you see arcing, sparking or smoking?" is 3.5 minutes into the automated call answering...
Replies
8
Views
733
Thank you, I had not considered the higher current in the good PEN, I must look as the building I work in has 3 or 4 supplies, there were separate...
Replies
3
Views
886

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top