Location
United Kingdom
Just a quick questiin can i use a 3 amp for a 2A fused connection unit the factory manuel is saying 2 amp full stop is this 100% or can i use a 3 amp i would of thought this would be sufficiant and then wired to a 6 amp breaker? Never done a alarm system before so making sure as dont want to pop any components
 
If the manufacturers specify 2 amp then yes that is the size you need to fit, fitting higher could damage the electronics under overload or fault conditions before the fuse operates. The 6amp at the breaker is protecting the cabling you wire to the fused spur... are you sure the 2amp is not applying to internal fuses in the panel itself, usually they do not ask for a 2amp in the fused spur supplying power to the unit thus 3amp will be fine... open the panel up, normally there is a fuse as part of the incoming terminals.
 
If you are a spark, best "open" up your profile so people can see your experience

As for fuses, as others have pointed out, you can buy 2A fuses (and others) so buy a few packs for your stock...
 
honeywell are wrong saying to use a sFCU. should be unswitched. so they're probably wrong about the fuse size also. i've been installing alarms since 1981 and without exception, all call for a 3A unswitched FCU.
 
I did know they have intenal fuses its the external we are on about thanks for reply guys girls

My asking about internal fuses was to do with @Michael Sands post #2. IMO a 3A fuse would be ok as the PCB has it's own fuses to protect that.
 
honeywell are wrong saying to use a sFCU. should be unswitched. so they're probably wrong about the fuse size also. i've been installing alarms since 1981 and without exception, all call for a 3A unswitched FCU.
I agree with this.

There is a fuse within the panel that protects all the equipment and a 3A fuse should protect your flex to panel perfectly fine...
 
Manufacturers instructions are guidance only and do not have to be followed, especially when they are wrong, as is the case here.

1. Although 2 amp fuses for plugs/fcus are available the only sizes officially recognised are 3 amp and 13 amp.
2. The fuse is to protect the cable which is 1mm not the appliance on the end of it which has its own internal protection.
3. What would happen in other countries where fcus are neither available nor compliant and circuits are protected by a 16 amp MCB?
 

Reply to Honeywell 2 amp fused connection unit in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

  • Question
Will it work? Yes. Will the trailer burst into flames? No. But code allows a remote structure (trailer) to be powered with ONE circuit, which...
Replies
6
Views
1K
All socket outlets up to and including 32A (which are commercial, not domestic) are required to be 30mA RCD protected. By the sounds of it you...
Replies
5
Views
986
The same socket can be used for different appliances, such as kettles... which will draw more than 5A The size of the cable determines how much...
Replies
4
Views
742
  • Question
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that...
2
Replies
29
Views
2K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
654

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks