I have just installed the above heating system controller on a Y plan all seems to work ok but the programmer is saying no signal and rf icon is flashing. The thermostat is coming in and out on tempeture, programmes are ok but this “no signal” is bothering me any ideas please
Thermostat is a DT92e
 
Yea as Lee says. Unbind and rebind and do a signal check first thing to do.

There pretty good but there’s a few things that might upset it like large metal objects(boiler) too close to prog or stat, foil backed plasterboard celotex etc. blocking signal

Had absolute murder with a Honeywell Evohome once and turned out to be interference from a Sonus speaker syestem.
 
I have disconnected batterys in stat which seems to reboot it. And turned power off of programmer to reboot that. It runs fine for a while but reverts back to no signal.i am using a wired cylinder stat which is not honey well would that make a difference?
 
I have noticed that if I go from constant hot water to constant heating switching the hot water off the 3 port valve is not moving!

Just moved temp on thermostat to below the room temp and boiler cut out. Put it up again and boiler comes on so rf is working. Yet programmer says it is not! Begging to think there is a fault in programmer
 
With all due respect BT and electrics are different.

When I wire a heating system I run through a series functional checks when ive finished, which involves turning stats up and down and watching values switch over.
If I suspect there is a problem with the room stat is prob link it out.

Have you connected the programmer up right ? Have you got call and satisfied (also refered to as "make" and "break") right way round on the Cylinder stat ?
Is the polarity right on your receiver ?

Out of interest have you wired the complete heating sytem in flexible cable ?
 

Reply to Honeywelly9420 sundial rf pack 2 in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
441
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
You need a wi fi switch that is compatible with your switchbot thermostats. Remove the SCR, use the neutral and live to power the wifi switch, and...
Replies
8
Views
1K
  • Question
Thanks davesparks. Looking at the diagram on the driver that's what I interpreted too, but I heard somewhere that the DALI system doesn't like...
Replies
2
Views
557

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top