Hi I'm looking for some advice, yesterday when exiting my hot tub I felt a slight electric shock when my foot made contact with the ground around the hot tub. I work as a cable jointer so a tingle is second nature to me so I double checked when in contact with ground and water I can feel a slight tingle in my fingers when isolated from ground I feel nothing. Today I put my multimeter onto a nearby earth terminal and probed the water to get a reading of 0.2volts. Im on a pme supply and have a cable running from a rcd to a isolated and then a feed to the tub. Any idea where this voltage could be coming from? And if installing a seperate earthing point with rods would solve the issue? Thankyou
 
How common are lost neutrals in your experience?

It is easy to slag of the network saying things should be better, but i bet you guys are working hard fire fighting most of the time as you say, leaving little resources left to upgrade
Not very common, the issue generally revolves around the cable I mentioned before (consac) it was a very badly designed and cheap cable that was laid from the 70's right through to the early 90's. There's cable thats been in the ground 100 years and is still in perfect condition but sections of it through other utilities and over load are starting to suffer but with that cable it tends just to blow a phase and become open circuit usually down to the lead plumbs failing and moisture tracking in
 
Shame as i personally feel TN-S is a much better system (despite the cost of an extra conductor)

The typical reasoning is the DNOs can no longer get TN-S cable as its not made anymore (although perhaps because the DNO stopped buying) if cable manufacturers can make 3 core copper concentric cable, i would presume they can make 4 core

I have also seen evidence of UKPN combining the E and N (PME) to repair sections of the old TN-S lead covered cable (I wonder if the tell the customers !)
TN-S or as us commoner cable jointers call it "split" is 100% still manufactured we actually stock it but for some reason the majority of the company will opt for its 3 core version due to it already being PME'd at the substation. Its actually easier to joint on the 4 core version than it is the 3 core so I have no idea why we do it the way we do but it's been the norm all the time I've been in the industry. As for customers or the electricians they would have absolutely no idea as to what the feed really is because if there has ever been a fault repair prior to there connection it's more than likely been combined on that section making their service pme
 
TN-S or as us commoner cable jointers call it "split" is 100% still manufactured we actually stock it but for some reason the majority of the company will opt for its 3 core version due to it already being PME'd at the substation. Its actually easier to joint on the 4 core version than it is the 3 core so I have no idea why we do it the way we do but it's been the norm all the time I've been in the industry. As for customers or the electricians they would have absolutely no idea as to what the feed really is because if there has ever been a fault repair prior to there connection it's more than likely been combined on that section making their service pme

Maybe the 3 core is cheaper, that's very interesting though, thanks for that, iv heard alot of people say the 4 core is not made, good to know it is

what is the common practice for petrol stations surrounded by PME, as far as i know PME is not allowed for petrol station forecourt, dedicated TNS supply or TT? just out of curiosity
 
Maybe the 3 core is cheaper, that's very interesting though, thanks for that, iv heard alot of people say the 4 core is not made, good to know it is

what is the common practice for petrol stations surrounded by PME, as far as i know PME is not allowed for petrol station forecourt, dedicated TNS supply or TT? just out of curiosity
Yes it will definitely be cheaper but I don't think it would be by much to be honest, the only difference between the cables is 1 less aluminium core so surely it can't add that much to the cost. As for petrol stations I've no idea, thinking back all the ones I've ever worked on through faults have been TNS supplies but whether they are true TNS I would highly doubt
 
The only time we get loss of neutral on our network in the North West is on certain type of mains cable (consac) its renown for it..... In 12 years of being a jointer I have never worked on a neutral fault that didn't revolve around a consac main.
Your insight into this area is much appreciated. I think much of the concern around TNC-S has resulted from the general lack of information within the electrical industry about it. The number of posts on this forum alone is a reflection of that.
As electricians we need to know what we are dealing with the pro, s and the con, s. To scaremonger is to do the industry and the public a disservice. To ignore the potential risks is equally wrong.
I would suggest the "crossing the road analogy" as mentioned by "Tim Howard" is the way to go. Educate people about the potential risks.
Similar to a TT system there are potential risks. It's essential that rcd, s are regularly tested to ensure safety.
 
IMO i think making a house a pme is most dangerous especially a pen fault.
Me thinks a system has a TNS is better for faults has it has a true earth not a one that being tagged to neutral, but you may think it all goes back to the grid.
You has well make all property's TT system in which you know will go earth
Ask the Spanish they been doing it for year, or any Eastern countrys are we behind or what.
 
Your insight into this area is much appreciated. I think much of the concern around TNC-S has resulted from the general lack of information within the electrical industry about it. The number of posts on this forum alone is a reflection of that.
As electricians we need to know what we are dealing with the pro, s and the con, s. To scaremonger is to do the industry and the public a disservice. To ignore the potential risks is equally wrong.
I would suggest the "crossing
I wonder what the odds on are on this.. Im on call today and about to make my way to a loss of neutral. The funny thing is the cable feeding these property's is a a split main and not PME ?
 
Ask the Spanish they been doing it for year, or any Eastern countrys are we behind or what.
There are trade-offs both ways. On TN systems you should be able to disconnect on the OCPD under earth fault conditions, so in that sense it is safer than relying on the RCD electronics. Of course you still want the RCD as most of the time it would disconnect on an electric shock type situation.

Down-side is the open PEN risk for outdoor equipment. In that past that was very little, probably a few floodlamps and often they are out of reach (OK, on fence another issue...)

TT avoids the issue of open PEN faults but then you need an RCD to achieve disconnection with any realistic earth rod installation. And you also have the issues of installing and maintaining rods in built up areas, etc. Of course you can reduce the impact of RCD reliability by having both a 100mA delay incomer and your usual 30mA instant "additional protection" RCDs/RCBOs so you don't have any single point of failure, but I would guess many TT installs just have the one RCD in any given circuit's path.

Any idea of how TT supplies are done in blocks of flats? Do they have a communal earth system?
 
What an interesting thread. I think @Samhhh may have answered more questions than had answers given ?.
It has been most informative and helpful to hear the other side of the coin on this from a cable jointers perspective. I hope he continues to linger around this forum!
 
Excuse quick diversion, then back to interesting TNS question!

In addition, one could argue that:
-GN7 says hot tubs outside should have section 702 applied.
-702.140.3.4.3 (ii) NOTE says:
"Where a PME earthing facility is used as the means of earthing [.....] it is recommended that an earth mat [...] of suitably low resistance e.g. 20 ohms or less , be installed and connected to the supplementary bonding."

Ok, I accept that's a recommendation based on a guidance note but had it been followed the (likely) problem in this thread wouldn't have happened.
Using an earth mat is a little bit different to a single earth rod
How much thought does anyone give as to where they decide to knock an earth rod into the ground, step potential under fault conditions could be interesting especially around a hot tub
The only time we get loss of neutral on our network in the North West is on certain type of mains cable (consac) its renown for it. The reason being that under the pvc the neutral/earth is full aluminium and as soon as water tracks in the aliminium oxidises over time and the neutral breaks down. The newer cables we install although they are cheap the neutral/earth's are split strands of copper and the odds over half of those strands corroding is very very low. In 12 years of being a jointer I have never worked on a neutral fault that didn't revolve around a consac main. We are however looking at a huge issue over the next few years with cables running above there capacity with the introduction of electric charging points and the amount of appliances in every home these days. The network is old and no one is willing to pay the money to update it. Everything is reactive maintenance in my industry not preventative.
Which DNO do you work for?
 

Reply to Hot tub electric shock in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

S
  • Article
Anyone plumb a DIY hot tub? I bought a used acrylic hot tub shell that I plan to sink into the ground in the backyard. The plan is to heat it with...
Replies
0
Views
210
siricosm
S
Well yes obviously, but if the transformer is indoors and your lights are 50m down the garden then it's very easy to need pretty big cables at...
    • Like
2 3
Replies
42
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top