Hot tub volt drop | on ElectriciansForums

Discuss Hot tub volt drop in the UK Electrical Forum area at ElectriciansForums.net

smity

-
Joined
Oct 15, 2008
Messages
70
Reaction score
22
Can i get away with 6mm SWA on a 50m run for a 32a supply to a hot tub? Cable will be burried.

I believe its very close to being over the 5% max Permitted?

Whats your thoughts, should i go up to 10mm?

Thanks
 
Checking e.g. Superlec cable prices, for 50m, the cost difference between 6 and 10mm2 SWA 3-core is less than ÂŁ30, which in the overall cost of the install and tub must be small change. So I'd just use 10mm2.
Yeah its not just the cost aspect, i already have a drum of 6mm and it would make the job easier as its running through the loft first (clipped up off the insulation).

50m is probably slightly over estimated, but i don't want to pull it in and have problems due to volt drop.

My calcs say under 50m is less than 5% but just wondered if you eould err on the side of caution?

Thanks
 
[ElectriciansForums.net] Hot tub volt drop
 
I noticed that's in fact for 90 degree SWA. I ran it again for 70 degree as it's maybe more likely the OP has that?
You get 5.078% or 11.68V
If it's just 1m shorter it's within 5%.
Also I know we have to use nominal voltage but at a more likely 240v it's 4.87%

Personally I'd pay the minimal extra for 10mm but I wouldn't shoot anyone installing this in 6mm either.
 
Customer would rather heat their hot tub than the soil between it and the house if explained to them, and 5% drop is the current 'fashion'. 2.5% for most om my career, and, for the sake of a few pounds, is what I still prefer to work to. Better for the pump motor starting performance, and the electronics might appreciate the reduced spikes.
 
Last edited:
Customer would rather heat their hot tub than the soil between it and the house if explained to them, and 5% drop is the current 'fashion'. 2.5% for most om my career, and, for the sake of a few pounds, is what I still prefer to work to. Better for the pump motor starting performance, and the electronics might appreciate the reduced spikes.
Think of it as undersoil heating. So you can walk from the house to the hot tub in your bare feet.
 
I ran it again for 70 degree as it's maybe more likely the OP has that
70 deg PVC - Can you still get that?

My software with a correction for being buried is a 'no' for 6mm, 32A at 50m. Are there any other derating factors to consider?
I thinks it is too 'close to call' and with relatively small price difference its 10mm for me, and no worries.
 
6mm 70C PVC in duct is easily 32A and for 90C XLPE SWA you could go thinner, but it will be the volt drop that makes the difference. Having said that, I doubt very much that a hot tub will suddenly fail at 5.5% drop!
 
If I was doing this for my own hot tub and happened to have a spare drum of 6mm2 SWA, I'd perhaps consider using it. But if this was for a customer, with a risk in the future of an observation on an EICR that the cable didn't comply, and having to explain why I'd not installed a big enough cable, ... I don't think so.
 
Cable difference is about ÂŁ90 (inc VAT) which is about 475 kWh at current domestic prices, so if going from 5.5% to 3.3% you are saving 2.2% then you have to spend ÂŁ4k on electricity to cover the cable costs (around 21.5 MWh).

Possible over a year or so, but I have no idea what the running cost of a stable heated sex pond is.
 

Reply to Hot tub volt drop in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
430
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
548
  • Question
If it is TT then you can use the armour of any of them as CPC but will almost certainly need an up-front delay RCD at the sub-main feed point to...
Replies
5
Views
973

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top