Yeah its not just the cost aspect, i already have a drum of 6mm and it would make the job easier as its running through the loft first (clipped up off the insulation).Checking e.g. Superlec cable prices, for 50m, the cost difference between 6 and 10mm2 SWA 3-core is less than £30, which in the overall cost of the install and tub must be small change. So I'd just use 10mm2.
Think of it as undersoil heating. So you can walk from the house to the hot tub in your bare feet.Customer would rather heat their hot tub than the soil between it and the house if explained to them, and 5% drop is the current 'fashion'. 2.5% for most om my career, and, for the sake of a few pounds, is what I still prefer to work to. Better for the pump motor starting performance, and the electronics might appreciate the reduced spikes.
70 deg PVC - Can you still get that?I ran it again for 70 degree as it's maybe more likely the OP has that
That is a good point, wonder what the cross-over point is when it pays for the bigger cable?Hot tubs run up a fair old electricity bill. In normal, non Covid times, I run two, so I should know.
I wouldn't want to spend 5% of that cost heating the ground, just to save a few pounds on installation.
Whether you can or not, unless the accessories etc to which it's connected are rated to run at 90°, 70° is all you can take it up to.70 deg PVC - Can you still get that?