Hot tub volt drop | Page 2 | on ElectriciansForums

Discuss Hot tub volt drop in the UK Electrical Forum area at ElectriciansForums.net

smity

-
Joined
Oct 15, 2008
Messages
70
Reaction score
22
Can i get away with 6mm SWA on a 50m run for a 32a supply to a hot tub? Cable will be burried.

I believe its very close to being over the 5% max Permitted?

Whats your thoughts, should i go up to 10mm?

Thanks
 
My software with a correction for being buried is a 'no' for 6mm, 32A at 50m. Are there any other derating factors to consider?
But that will be a no for VD reasons, not because the current carrying capacity of 6mm² SWA is too low. And the VD will be calculated with the resistance of the cable at 70° or 90°.

Other derating factors would give the cable a lower CCC, but as I said, that's not the limiting factor here

There might be a converse to consider though - what ambient temperature does your s/w assume? If you can get the temperature down then the resistance comes down - it's about 25% lower at 10° vs 90°.
 
But that will be a no for VD reasons,
Without stating the obvious, yes of course??
If you can get the temperature down then the resistance comes down -
If you can regulate the temperature in an attic void and underground?
We don't know the full facts and whilst the cable may be clear of insulation the attic void if south facing could be much higher than 30deg in the summer when the hot tub is most likely to be used.

If the OP can justify using 6mm then fine with me! but he has come on this forum for others views and is probably more confused than before! :)
 
Thanks for all your replys and input ? its looking like its 45m which seems like it should be ok using 6mm with a 4.5% VD

Now i have unearthed another query with it being a PME system.

I have seen lots of conflicting information regarding how this should be tackled and I believe there are 3 options (probably more)

- 32a Type c from split RCD board

Option 1 - use the PME earth for the entire job as this isn't a swimming pool but a "built to product standard" hot tub so doesn't fall under section 702 - no exposed parts etc

Option 2 - PME earth covers supply cable to isolator but then is stopped there (Plastic gland and heat shrink armourings), Earth spike local to isolator and then use a TT earth from the isolator tail to the hot tub

Option 3 - PME earth covers supply to an external enclosure and 30mA RCD, TT spike from this point to isolator and tail but then you have 2 RCD's covering the circuit.

Anyone have any input on this?

Ive attached a document ive found on NICEIC site saying PME is fine but just wondered on your thoughts.

Thanks again ?
[ElectriciansForums.net] Hot tub volt drop
 
I have seen lots of conflicting information regarding how this should be tackled and I believe there are 3 options (probably more)

- 32a Type c from split RCD board

Option 1 - use the PME earth for the entire job as this isn't a swimming pool but a "built to product standard" hot tub so doesn't fall under section 702 - no exposed parts etc

Option 2 - PME earth covers supply cable to isolator but then is stopped there (Plastic gland and heat shrink armourings), Earth spike local to isolator and then use a TT earth from the isolator tail to the hot tub

Option 3 - PME earth covers supply to an external enclosure and 30mA RCD, TT spike from this point to isolator and tail but then you have 2 RCD's covering the circuit.

Anyone have any input on this?
If you listen carefully you might hear a collective groan as this subject has been discussed a lot recently!
Brief comments:
Option 1 is compliant but has issues. I used to do this but wouldn't now. See recent thread on tingly feet when getting out if you want a long read. [Also IET Guidance Note 7 (Special Locations) does have stuff about hot tubs outside coming under Section 702, as a recommendation)
Option 2 - What I'd do.
Option 3 - Also Fine but I'm missing the gain over option 2 - complete pot luck which RCD would go? If you could avoid upstream RCD this would clinch option 2 for me.
 
If you listen carefully you might hear a collective groan as this subject has been discussed a lot recently!
Brief comments:
Option 1 is compliant but has issues. I used to do this but wouldn't now. See recent thread on tingly feet when getting out if you want a long read. [Also IET Guidance Note 7 (Special Locations) does have stuff about hot tubs outside coming under Section 702, as a recommendation)
Option 2 - What I'd do.
Option 3 - Also Fine but I'm missing the gain over option 2 - complete pot luck which RCD would go? If you could avoid upstream RCD this would clinch option 2 for me.

Thanks for your reply, its much appreciated.

i understand the groans and i have spent a lot of time reading the other threads and various other documents trying to find the best option, also spoke to other electricians and everyone seems to have a different view.

I agree with you on option 2 being the better option and most probably what i will go for TBH unless anyone has a reason why this wouldn't be acceptable.

Thanks
 
Can i get away with 6mm SWA on a 50m run for a 32a supply to a hot tub? Cable will be burried.

I believe its very close to being over the 5% max Permitted?

Whats your thoughts, should i go up to 10mm?

Thanks
What do your cable calcs tell you? if of course you have bothered doing any.
 

Reply to Hot tub volt drop in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
454
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
549
  • Question
If it is TT then you can use the armour of any of them as CPC but will almost certainly need an up-front delay RCD at the sub-main feed point to...
Replies
5
Views
983

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top