So hot tubs, would you use the pme supply and get that slight tingle when getting out or rod it? Can't find a reg on it so it's a bit unclear. Your thoughts please!! :)
 
Hi E54,

As far as PME goes, I think this probably the time to consider TTing it, as you would for caravan pitches etc.

Edit: just read your post saying basically the same thing, lol

It's not so much the PME, more in the fact that a person with wet bare feet on bare ground or a conductive concrete, that is at or near to true ground potential, with an electrical ground potential also being present. There is a chance (remote maybe) of a step voltage between the two potentials....

The chances of a broken neutral on the PME, i wouldn't particularly consider, you'll be lucky to see one real instance in a lifetime...
 
Thanks for all the replies found a sticker on the tub to earth rod the install, 3 rods smacked in the ground later got it to 13ohms..... Dipped my hand in to check water temp and I got a tingle!!! Think i have narrowed it down to heater leaking to earth a little so I'm going to ir the element tomorrow and more importantly not use it for now lol
 
Sounds as if you have an American hot tub there, if you have found a sticker to that effect. American hot tubs often come with a supplied 8 foot earth rod when new...
 
Right to all of those interested I have tried the rod and pme and you get a tingle and now have made the tub TT and tingle has gone, rod is 13 ohms so all good to go! Must be a slight potential difference between true earth so to speak and the suppliers earth, that's all I can think of....
 
It's not so much the PME, more in the fact that a person with wet bare feet on bare ground or a conductive concrete, that is at or near to true ground potential, with an electrical ground potential also being present. There is a chance (remote maybe) of a step voltage between the two potentials....

The chances of a broken neutral on the PME, i wouldn't particularly consider, you'll be lucky to see one real instance in a lifetime...

That's what I was trying to say lol didnt realise you has already said it :)
 

Reply to the thread, titled "Hot tubs...." which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top