O

Octopus

Victorian house - just rewired.

EIC provided .......

Description of works "total rewire of all circuits. Dead tests only"

Speechless

Rant over..................
 
Maybe that's for NICEIC testers who aren't confident about testing live.....or don't know what WTF they're doing.
Nah, impossible, how can you install a circuit and not do a live test on it? Strima is having a laugh with us, you'll see he will come on in a minute with a cheeky grin, surely lol.
 
Where do you get this information? I am happy to talk to the local NICEIC engineer about your views when I go to a meeting next time. Can you E-Mail me your membership number and company registration number so I can ask them to look into your claims?
I got it direct from my area engineer around three years ago.

Doesn't mean to say I listened to him does it?
 
Nah, impossible, how can you install a circuit and not do a live test on it? Strima is having a laugh with us, you'll see he will come on in a minute with a cheeky grin, surely lol.
Where did I say I don't do live testing?
 
I got it direct from my area engineer around three years ago.

Doesn't mean to say I listened to him does it?
Well to be fair I do like and respect you Strima and always have, but I would suggest your engineer is a numpty and lets be fair you know it as well lol, so based on that please don't back the muppet up, whats his name so I can humiliate him at the next NICEIC meeting I attend?
 
Where did I say I don't do live testing?
I never said you didn;'t I was replying to your comment you heard that you didn't have to, it is my gloucestershire accent that came across all wrong :D
 
I never said you didn;'t I was replying to your comment you heard that you didn't have to, it is my gloucestershire accent that came across all wrong :D
Take the cider bottle out of your mouth then... :D

As for my AE, he's retiring this year so I'll let him go peacefully...
 
I read, heard or somehow acquired information from god knows where, Rcds will not require testing on the job in times to come
The tests by the manufacturer prior to sale are to suffice ;):)

So what is the point of the schedule of inspections ?

Got my annual assessment soon.

Think I will present my assessor with a schedule showing only dead tests and see what he says....
 
I read, heard or somehow acquired information from god knows where, Rcds will not require testing on the job in times to come
The tests by the manufacturer prior to sale are to suffice ;):)
Was reading about the Chinese made MCBs made for (MK employee telling his dad - reliable source!) that then get tested by the UK base and get chucked because they fail. I think we do need to keep testing RCDs because even fresh out of the box they can be faulty and lets face it - it’s us who’ll have to return and we’ll never see that money or time again and it just makes us look bad.
 
The certificate had a registration number on it but no logo ..........................

a quick google search revealed ......................


Yes, you've guessed it ...................... NICEIC contractor.
 
The NICEIC have been making a big thing about working live for some time now.

In Certsure's Magazine Winter 2017-18 issue, there is one technical article on 'Prospective fault current in domestic and similar properties'.

It describes consumer units to BS EN 61439-3, single phase supply 250V, via a service cut containing an HBC fuse to BS 1361 Type II, not exceeding 100A.

It also states the maximum prospective fault current declared by DNO, suitably connected to take account of service cable length, does not exceed 16 kA.

It demonstrates the tests, and reasoning for.

It finishes with a section on EaWR 1989 & live testing, and a section headed Conclusion. In the Conclusion 'and where conditional rating is applicable, it follows that carrying out an unnecessary test to determine the prospective fault current at the origin, or indeed elsewhere in the installation, is unjustified live working and hence could be seen as a breach of Reg 14 EaWR 1989'.

I think I've done a fair precise of the article, the issue (magazine) is not freely available as a download at the moment. Perhaps this is one of the live tests (not to carry out) your colleagues spoke of?

Have to say, when I've had my Elecsa assessments, I've been asked to demonstrate these (live) tests.
 
re working "live"

plugging in your MFT to a socket to test the Zs is no different than plugging in your mobile phone charger ..................

It’s very different, the mobile phone charger is an appliance connected between L and N, if it’s not done correctly the phone won’t charge.
The tester is deliberately passing a current via the cpc, if it’s not done correctly (dead tests passed, cpc properly connected to the means of earthing) it can cause a lethal voltage to appear on exposed parts connected to that cpc.
 
What a load of tripe from some on here. If some stopped the constant, boring NICEIC bashing and focused on the real issue perhaps matters would be clearer.
NICEIC area engineers certainly encourage contractors to minimise the use of “live” testing wherever practical, simply to reduce risk of harm, eg live tests at a ceiling rose, as dead tests will prove the existence of a cpc, polarity etc. Is plugging in a tester to measure Zs a live test.... of course it is but it presents no risk to the person carrying out the test.
I totally agree that some people/organisations use the H&S card too frequently, but our area engineer is certainly not one of them.
Is live testing the same as live working????
As for the OP, I would certainly be querying the EIC, especially if the installation has rcds/rcbos.
 
In Certsure's Magazine Winter 2017-18 issue ... It finishes with a section on EaWR 1989 & live testing, and a section headed Conclusion 'and where conditional rating is applicable, it follows that carrying out an unnecessary test to determine the prospective fault current at the origin, or indeed elsewhere in the installation, is unjustified live working and hence could be seen as a breach of Reg 14 EaWR 1989'.
Thanks for posting @Midwest :)
I have 2 thoughts - pfc testing is to establish less than 16kA and 6kA (MCB for example) and DNO only comment on 16kA at source. Note they do not certify it's less than 16kA so we test it where that is possible. Or have I missed something?
Next one - saying pfc tests "could be seen as a breach of reg14" is akin to saying my butt "could be seen" as attractive, but that is also unlikely :)
 
If I try to enquire ze from the DNO for tncs they will say 0.35 ohms which is ridiculous and may lead to unnecessarily larger cables installed for circuits to comply with ADS
Maximum should be 0.35 Ohms for PME, 0.8 Ohms TNS but I seem to think some DNOs have revised PME maximum to 0.20 Ohms for new connections.
 

Reply to How can anyone think this is acceptable ... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
My older card has it but my newer card doesn’t
    • Like
Replies
1
Views
470
  • Question
Most RC Model systems work on a bus system now days so minimal wiring, Transmitters are available up too twenty channels and more so that is not...
Replies
8
Views
453
  • Question
If they got a shock then something cannot have been isolated.
Replies
7
Views
1K
  • Question
It looks like FP200 style cable...
Replies
10
Views
2K
Thought I'd update this. Finally had my assessment today. I chased them on Friday morning as it'd been about 10-12 weeks since I'd actually made a...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks