How do we solve the long meter tail problem? | Page 3 | on ElectriciansForums

Discuss How do we solve the long meter tail problem? in the UK Electrical Forum area at ElectriciansForums.net

Joined
Aug 17, 2019
Messages
94
Reaction score
46
Location
Broxbourne
Just seen a you tube video by Artisan, he mentions there is a 15 meter run that goes in the fabric of the building from the meter/100amp cut out to the consumer unit.
it started a debate as to whether to code it a c2 or c3. The question that I have is how would you fix/solve the problem?
the house was a relatively new build as well so how did it pass initial verification?
Discuss.....
 
mechanical protection = sheath

I'm not saying it's fact, I don't know more asking for BS 7671 reference that Singles not in
containment require mechanical protection(sheath) and own Earth(CPC) like 6241Y?- it's something I've heard before.
 
mechanical protection = sheath

I'm not saying it's fact, I don't know more asking for BS 7671 reference that Singles not in
containment require mechanical protection(sheath) and own Earth(CPC) like 6241Y?- it's something I've heard before.

Yes the basic insulation of cables should not be exposed in a finished installation (526.8)

Yes containment such as metal trunking and conduit provides mechanical protection and may be used as a cpc. It would need earthing regardless of use as a cpc or not (411.3.1.1 and 543.2)

Yes a cpc should be present at all points and accessories in a circuit (411.3.1.1)

I know of no reg which states sheathed cables need to have integral cpcs.
 
Yep - normally each cable without containment needs mechanical protection and it's own earth like 6241Y doesn't it?

No a cable does not have to have a protective conductor contained within it to be installed.
You can install insulated and sheathed singles such as 6181Y or single core H07-RNF with a seperate protective conductor.
 
got me thinking so I just did a search I actually can't see any single-core cable for standard circuits i.e 1.5mm or 2.5mm/lighting sockets etc with a sheath and without a CPC ? am I missing something?
 
Last edited:
got me thinking so I just did a search I actually can't see any single-core cable for standard circuits i.e 1.5mm or 2.5mm/lighting sockets etc with a sheath and without a CPC ? am I missing something?
It wouldn't be common, or cost effective, to wire entire lighting and sockets in PVC/PVC singles. I've not come across any PVC/PVC 2.5mm, it would likely be a bit of a pointless cable as 2.5 T&E will do what is required at less cost.

It's very common in these parts (Northern Ireland) to use PVC/PVC 1.5mm single brown, blue, either with CPC or not for lighting circuits, but they would be for switch line drops to multigang switching etc, the majority of the circuit would be in T&E and looped at the rose. I generally loop at the switch and use 3 core and earth for 2 way, but I'd be in the minority here doing that. For alterations and additions the singles & singles and earth are really useful.
 
got me thinking so I just did a search I actually can't see any single-core cable for standard circuits i.e 1.5mm or 2.5mm/lighting sockets etc with a sheath and without a CPC ? am I missing something?

6181Y is available from 1.0mm to 35mm or maybe 50mm.
I see it all the time in existing lighting circuits.
 
Sorry I'm asking 1.5 2.5 etc
With Sheath
Without CPC

obviously it common without sheath and fairly common with sheath and CPC 6241Y

trying to prove singles with sheath don't need a CPC on standard circuits not talking about 16mm+ tails etc.
 
Sorry I'm asking 1.5 2.5 etc
With Sheath
Without CPC

obviously it common without sheath and fairly common with sheath and CPC 6241Y

trying to prove singles with sheath don't need a CPC on standard circuits not talking about 16mm+ tails etc.
A sheath has no bearing on any requirement for a cpc. The sheath is there solely to provide mechanical protection to the insulated core of the cable and nothing else.
 

Reply to How do we solve the long meter tail problem? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top