E

egginyourface

Evening all,

When testing r1 + r2 do you connect live to earth bar, link it at the end of the circuit or do you have someone at the end helping you?

whilst testing Today I was wondering is there a quicker way to do it apart from the long lead method as I prefer r1+r2
 
Piece of cable with 2 crocodile clips.one on the earth bar,one on the bus bar .switch on the mcb that is being tested. you get your reading and check your labelling at the same time

Next circuit,off with one mcb,on with the next and not a screwdriver in sight
 
Long lead method? You must be a glutton for punishment....
30cm length of 1.5mm 3-core flex with all cores connected to a croccy clip at each end gives you negligible resistance. Clip one end to the line conductor you are testing and the other end to the earth rail (with cpc connected). Now you can test R1+R2 effortlessly at each point.
Seriously, get yourself a copy of GN3.
 
I was thinking about the crocodile clip methods as it would speed things up. Only problem is energising circuit whilst its still comnected.

I usually link live into earth terminal but hate doing this for some reason.
 
They sell them croc clips on ebay in packs of 10 for next to nothing. Just remember to test resistance of lead and deduct it from your r1 & r2 reading.
 
Long lead method? You must be a glutton for punishment....
30cm length of 1.5mm 3-core flex with all cores connected to a croccy clip at each end gives you negligible resistance. Clip one end to the line conductor you are testing and the other end to the earth rail (with cpc connected). Now you can test R1+R2 effortlessly at each point.
Seriously, get yourself a copy of GN3.

What's afoot???
 
Piece of cable with 2 crocodile clips.one on the earth bar,one on the bus bar .switch on the mcb that is being tested. you get your reading and check your labelling at the same time

Next circuit,off with one mcb,on with the next and not a screwdriver in sight

don't like that. any resistance within the MCB will give false readings. i take the L out of the MCB and clip from the cable end to the E bar.
 

Reply to How do you test r1+r2? Any tips on doing it faster in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
933
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top