Piece of cable with 2 crocodile clips.one on the earth bar,one on the bus bar .switch on the mcb that is being tested. you get your reading and check your labelling at the same time

Next circuit,off with one mcb,on with the next and not a screwdriver in sight

How did you get the front off of the CU then :tongue3:
 
don't like that. any resistance within the MCB will give false readings. i take the L out of the MCB and clip from the cable end to the E bar.

A very quick and simple action tel is to take a reading through the mcbs
It would indicate any high resistance mcb, this resistance is also part of the earth loop which is a bonus

Unless circumstances don't permit,taking out conductors from the mcb (which can create a problem where none existed previously, if the tester fails to remake the connection correctly)is a waste of time and needless disturbance where none may be needed
 
How did you get the front off of the CU then :tongue3:

I hold my hands up to that one
[ElectriciansForums.net] How do you test r1+r2? Any tips on doing it faster
[ElectriciansForums.net] How do you test r1+r2? Any tips on doing it faster
 
I was always taught not to disconnect stuff if it was not needed for the reason above when it came to testing. I would always test through a mcb for high resistivity though to ensure a good connection
 
my new megger tester has an r1+r2 Zs test mode, it saves the Ze reading and just subtracts it from the Zs, what do you guys think of that as I always thought of that as a cheats way of testing, but its certainly quicker
 
my new megger tester has an r1+r2 Zs test mode, it saves the Ze reading and just subtracts it from the Zs, what do you guys think of that as I always thought of that as a cheats way of testing, but its certainly quicker
Why would you want it when measuring Zs?

Presumably you already have the R1+R2 value and have already added Ze .
 
Well what that setting suggests to me is that you can obtain the r1+r2 value by doing a Zs test, which is easier and quicker, but it seems like a cheat
 
Well what that setting suggests to me is that you can obtain the r1+r2 value by doing a Zs test, which is easier and quicker, but it seems like a cheat
But you must have already done the Ze.

I take it it can't work out what is R1+R2 and what is Ze from a single measurement.

Plus - it does not detect parallel paths so R1+R2 will be lower than the actual value
(unless you enter Zdb to be deducted).

Just being picky as Flukes have always given you R2 when measuring Zs but this obviously includes the distributors earth.
 
Yes but I need to do the ze anyway, parallel paths are the only problem with that I suppose, but do you think that's an acceptable way to obtain r1 +r2? because its so much quicker
 
getting the value of R1+R2 from Zs is OK (IM0) on a EICR where the circuit is energised already, but on initial verification, you must measure resistances before energising.
 

Reply to How do you test r1+r2? Any tips on doing it faster in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top