Hi guys. I need to check if I have a ring or 2 radial running from a fuse. I have an old wylex fuse box in which someone has put a blue 15amp fuse in a red 30amp carrier.
If I disconnect the 2 cables and check for continuity of the 2 lines then the 2 neutrals will this tell me if I have a ring or am I missing something ?

Thanks in advance guys
 
It's not that simple mate, checking for continuity in that way will only prove that the two legs are interconnected at some point. They could be joined half way along but not be a ring. There is a specific test for this, but it is not something a none-spark should really be doing. I assume you are not a spark, judging by the question. Do you have an MFT?
 
Agree with above and you show you have no electrical qualifications. It would be a routine test for an electrician then you can fit the correct fuse and shield.
 
It's not that simple mate, checking for continuity in that way will only prove that the two legs are interconnected at some point. They could be joined half way along but not be a ring. There is a specific test for this, but it is not something a none-spark should really be doing. I assume you are not a spark, judging by the question. Do you have an MFT?

Thanks for the reply.
Your right pal I'm not a spark but I'm not a numpty either if you know what I mean. Yes I do have a multi meter. In your opinion is it something I can do with the help of good people like yourself ?
For reference this is not for a job but just to help my pensioner in laws out as it appears someone has, like I said, put a 15a fuse into a 30a carrier. I just want to sort it for them so they don't lose all sockets as they currently have done 4 times in the last 3 weeks.
Thanks for any constructive advice I really do appreciate it.
 
To verify if it is a ring, you need to access every socket outlet on the circuit in turn (you will likely have to unscrew them all), after making temporary connections in the CU. You also need to know how to interpret the results obtained from your 'multi meter'.
 
You really need a continuity tester and whilst I understand wanting to help the in laws the circuit needs correct testing and it would be difficult to give instructions to a non qualified person without the correct meter.
 
Thanks for the reply.
Your right pal I'm not a spark but I'm not a numpty either if you know what I mean. Yes I do have a multi meter. In your opinion is it something I can do with the help of good people like yourself ?
For reference this is not for a job but just to help my pensioner in laws out as it appears someone has, like I said, put a 15a fuse into a 30a carrier. I just want to sort it for them so they don't lose all sockets as they currently have done 4 times in the last 3 weeks.
Thanks for any constructive advice I really do appreciate it.
 
For advice as to suitability of the test. I rather hear from someone who does the job than a teacher who may have all the gear and no idea. Their is no substitute for real life experience
 
Why bother coming here then, when you think you can trust You Tube?
Just trying to show the OP the complexity, of a RFC test and the need for the correct equipment, a multimeter is no good for this test, not something for what is a DIYer or in this case a Handy man, who in all honesty shouldn't be fluffing around with something he has very limited knowledge, these videos are very informative for trainees etc, absolutely not to be used by non sparkies
 

Reply to How to check if a fuse feeds a ring final or 2 radial circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
289
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
792
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
822

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top