How to ensure correct phase rotation on generator
Hi all,
Might seem like a silly question, but I have a client who wishes to install a 3 phase generator to back up the supply of an office building.
The client approached me and said before the job commences, he wanted to establish if the phase rotation of the generator would match the phase rotation of the building. I think this request is more for reassurance for him than anything.
I was a little confused at first, and still am really. I told him I could test the phase rotation of the building as it is now. And that the only way of ensuring that there's no crossing of phases etc is by opening generator and identifying which cables are which, ie L1,L2 and L3, and connectors them accordingly to changeover switch.
I haven't seen the generator yet so not sure if leads must be made up or are supplied. But does anyone find this a little odd, or have any solutions to his insisting the phase rotation of generator matches the building?
Its largely as simple as you think. The building may not be 123, so the generator would have to be connected to match whatever the building is. Depending on the distribution network on-site , i have seen where sub-boards have been connected 321. So wherever you intend to connect the Genny just check what current rotation is an match it to the generator.
Where I used to work (in IT), we had reversed rotation on the supply which made it interesting when contractors didn't get the message. Mind you, we had a chiller installed where one of the motors (there were 3 compressors and 3 fans) was also reverse connected.
But isn't the OP's issue "just" a case of checking the rotation for the building, then fire up the genny and check that, then connect the genny either direct or reversed as required ?
123, 231 , 312 are all clockwise rotation
321, 213 , 132 are all anti clockwise
For all applications that I can think of, it makes no difference which of the 3 possible combinations for each direction are used.
Even if you are synchronising 2 supply’s then it should be ok as long as the direction is correct.
Indeed, as long as the supplies are independent - as would be the case with a standalone genny. Indeed, without an external reference, it would be impossible to differentiate them if just handed 3 unlabelled terminals.
123, 231, 312 choice does become important if the supplies are synced elsewhere - as would be the case if the site had two grid derived supplies.
DNOs (and National Grid) have to be very careful as there are many loops in the network - so maintaining correct phasing is critical.
Making a rash assumption that if the incoming supply differs from 1-2-3 and if so has been corrected at the very first point of termination in order to standardise the rest of the downstream building, then the AMF/changeover system will also be seeing 1-2-3 regardless of what's at the DNO intake. Hence, just take 1-2-3 from the generator.
After double checking by measurement, naturally 😉
An Buachaillín Bán,
Rockingit,