I have been told in the past ( All be a builder that wanted the job instead ! ) that it is illegal to mole cables underground as you can not install a marker tape with it !
What thoughts do others have on this one ?
Thanks in advance if you reply .
Without additional protection such as a flexi-conduit or ducting, the cable should be surrounded by sand to eliminate stones piercing the sheath.
I am a "belts and braces" man so always install underground cable in a conduit.
This is part of my question really , i have never seen a utility company do this when i have seen them do road crossings in the past ?
We tend to nearly always pull expander's up the mole and then duct it before pulling a service , this approach is very labour intensive but the right one in my opinion !
It would be good to know for definite though what the minimum requirement would be ?
Regs are that armoured cable is buried to a suitable depth with marking tape or a marked cover above it (reg 522.8.10). Good working practice is to lay the cable on 100mm of sifted sand at a depth of 600mm, then a further 150mm of sifted soil or sand is poured over the cable. Then a marked cable tile is placed on the sand followed by the backfill.
If the cable runs through a suitable ducting or conduit then that method of protection should be suitably identified. I think Jase's suggestion of orange conduit would cover this if it was impossible to place marking above the cable itself.
seen them put under motorways and apparently they have to run at 90 degrees to the road and they put a concrete marker post at each end, and of course marked on digging prints,as the idea of moling under a mway is to avoid disruption opening it up.