T

theugly

hi all, just a silly question because i never replaced an earthing conductor before,

just finished an inspection. the earthing conductoris only about 6mm. i am thinking to upgrade it to 16mm. the end of the conductor is taped in the supplier's thick conductor. I think it is a TN-C-S system, the outside metal of the trunk is for neutral and earth. i untaped it and found the end of the earhting is buried in some dark color painting, can i forced the earthing out and replace it straightaway?

thanks a lot,
 
Last edited by a moderator:
Hi pal, not sure I would not want to be taking it off the incoming supply conductor, (think the term is "sweated on"). Have seen the conductor taken from the incoming supply into an Earth block and then 16mm main earth to board/10mm bonding to services etc.

Regards WA
 
I think you are talking about a TN-S system there mate.

Your probably looking at the swa from the incoming supply which is normally used as an earth for a TN-S system.
Did you say you have just done an inspection ?

Sav
 
Hi mate
What size are the tails
If its TN-C-S then the earthing conductor has to be 16mm if carrying out alterations and additios

but you say the existing earthing conductor is connected to the suppliers conductor

If you are unsure mate what system it is or what to do then my best advice would be to contact the DNO to ask what type of earthing system it is
and if you are thinking of replacing this maybe you could ask the dno to upgrade as you shouldnt be messing with the DNOs cut out fuse or equipment they will fit a isolator and upgrade existing tails from cutout to meter and then to main 100A isolator switch and they will fit a earthing conductor to there equipment either by pme or tns

others more experienced may advise you better

what size are the Main protective bonding conductors to the water and gas

If your only carrying out a PIR then you only are inspecting the existing installation and should record observations and code as appropriate any code 1s need urgent attention or immediatly isolate the defective part code 2s require improvement
 
from all the replies do you all mean that 6mm is ok from supply to earthing block, as long as from earthing block to consumer unit is16mm?
 
That will be a tn-s system and is the suppliers earth to met, so providing you have a ze lower than 0.8 ohms and the consumers earth from the met to the consumer unit is of an adequate size its of no concern to your pir. If on the other hand the small wire is coming straight off the sheath into the consumer unit i usually reterminate into an external met and take a 16mm into the cu it will then satisfy the cert as the consumers main earthing conductor is of the right size. you should neva mess with there incoming cable, if you take a ze reading and it doesnt satisfy you contact the supplier to upgrade hope this may help.
 
on a tnc-s earth is taken from the neutral conductor at the supply cut out, u may somtimes come across and installation where it has a wire from the sheath and the neutral to the met this would be recorded as a tnc-s and is where the sheath of the cable has broken down over the years and the resistance to earth has become to high so the supplier has upgraded the system to tnc-s and left the sheath earth terminated.
 
thanks all, last question, how to distinguish between tn-s and tn-c-s?

Are you kidding me here?
You've done a PIR which requires 'an above average knowledge of BS7671' and you can't identify the earthing system?
 

Reply to how to upgrade the earthing conductor? in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top