You can even find diagrams on DIY sites now !!!!!! http://www.diynot.com/wiki/electrics:earthing_supply_types_and_bonding:earthing_arrangements unbelievable.
Last edited by a moderator:
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss how to upgrade the earthing conductor? in the Talk Electrician area at ElectriciansForums.net
That will be a tn-s system and is the suppliers earth to met, so providing you have a ze lower than 0.8 ohms and the consumers earth from the met to the consumer unit is of an adequate size its of no concern to your pir. If on the other hand the small wire is coming straight off the sheath into the consumer unit i usually reterminate into an external met and take a 16mm into the cu it will then satisfy the cert as the consumers main earthing conductor is of the right size. you should neva mess with there incoming cable, if you take a ze reading and it doesnt satisfy you contact the supplier to upgrade hope this may help.
i may be inaccurate here, but theoretically the protective device, usually a 1361, will blow long before the fault current gets anywhere near it's rated breaking capacity of 16kA. it's a very rare occurence for a fault current to develop upstream of the circuit protective devices, although not unknown.just to come in on this at a late stage on what has obviously been an interesting discussion. It should be remembered that unnecessarily upgrading earths could potentially cause problems in itself as this could lead to higher PEFCs that might exceed the breaking capacity of the protective devices so they can not clear the fault safely. It really should be checked properly and not just immediately assumed that bigger must automatically be better.
As I've already stated, sizing of protective conductors is by either SELECTION or CALCULATION!!
If it's a new installation then selection can be applied at the design stage. This chap has attended an already existing installation and is thinking about upgrading the earth when it most likely is not necessary.
If you don't know how to do the adiabatic then say so!!!
Sent from my iPhone using Tapatalk
Fair comment.
But selfishly let me take another view.
A few months ago I started a thread similar to this where I went to a customers house.
British gas where to install a new central heating system but refused to do it cause the main earthing conductor was 4mm straight into the MET on a TNS system.
I'm still in the process of awaiting DNO to come out so it can be changed over.
Now although the Ze was fine and PFC I questioned the inadequacy of the size that would it take the fault current. Would this mean I shouldn't be changing this too and telling British Gas to stop being so silly?
i may be inaccurate here, but theoretically the protective device, usually a 1361, will blow long before the fault current gets anywhere near it's rated breaking capacity of 16kA. it's a very rare occurence for a fault current to develop upstream of the circuit protective devices, although not unknown.