That question is almost as bad as situations i get with clients, one of the most important info missing, lol
Anyway as for power, this can be expressed as KVA or KW, however key info missing again, so you can only provide KVA.
Try ChatGPT and ask it to calculate KVA based on a load current of 35A and supply voltage of 400V.
That would have been a great question and a good use of BS7671, shame - good luck
 
Upvote 0
Sorry - am I missing something here? To me it seems that everything is there with the exception of a distance?
 
Upvote 0
How would you work out power then?
It doesn't ask for power. It asks for design current (which is stated at 35A per ph).

So our cable needs to be in a ratio /10m length which allows for the Max Zs of a C40 RCBO - so that's Ze (0.35) + x, where x is informed by the R1R2 value of relevantly sized cables and voltage drop for conductor sizes at load and voltage, less any derate factors. I'm not going to get out the tables as we don't do other people's homework on here....
 
Upvote 0
It is asking for stage 1 to select a cable size by using the design current, the rating of the protective device and the installation method. You have been given these three factors to work with things like volt drop, R1+R2, Zs, adequacy of cpc are done after stage 1 to ascertain if the cable selected is adequate.
 
Upvote 0
It is asking for stage 1 to select a cable size by using the design current, the rating of the protective device and the installation method. You have been given these three factors to work with things like volt drop, R1+R2, Zs, adequacy of cpc are done after stage 1 to ascertain if the cable selected is adequate.


I know it isn't asking for power.

But I normally work in by p/voltage. But I don't know what that P is. Then In is greater than IB . And I carry on after that
 
Upvote 0
You are complicating things. This is stage 1 of circuit design just concentrate on that you only have one calculation to do and that is applying the correction factor for the buried cable to In, once you have this you can select a cable.
 
Upvote 0
What Westy said.

But if you insist.... let's look at it from another angle, using the traditional beer/head analogy for pf. It's a milking parlour - pick full fat (4%), semi (2%) or skimmed and go with that.
 
Upvote 0

Reply to the thread, titled "How to work out the power?" which is posted in Electrician Courses : Electrical Quals on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Thread starter

Joined
Location
Yorkshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
How to work out the power?
Prefix
N/A
Forum
Electrician Courses : Electrical Quals
Start date
Last reply date
Replies
12
Unsolved
--

Thread Tags

Tags Tags
None

Thread statistics

Created
shocksl,
Last reply from
Rockingit,
Replies
12
Views
121

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
Back
Top