Read the question….. ALL of the question….
Unless we assume unity .............Sorry - am I missing something here? To me it seems that everything is there with the exception of a distance?
It doesn't ask for power. It asks for design current (which is stated at 35A per ph).How would you work out power then?
It is asking for stage 1 to select a cable size by using the design current, the rating of the protective device and the installation method. You have been given these three factors to work with things like volt drop, R1+R2, Zs, adequacy of cpc are done after stage 1 to ascertain if the cable selected is adequate.
Stage 1 is asking for Iz, if gives you Ib and In.I know it isn't asking for power.
But I normally work in by p/voltage. But I don't know what that P is. Then In is greater than IB . And I carry on after that
Reply to the thread, titled "How to work out the power?" which is posted in Electrician Courses : Electrical Quals on Electricians Forums.