Morning all, been pondering quite a bit lately about Hybrid circuits,especially 13amp socket circuits, the likes of lolly pop rings etc.

I don't want to get into arguments about the pros and cons and why people install them, that's been done to death, whether, I personally agree with this method is neither here nor there, no, my question is, " how are these circuits tested, and how are the results entered on the installation certificate?" for example if you have installed a lolly pop ring how is that described? as a ring or a radial.
 
A very good question.

With a lollipop ring final I would enter r1 rn r2 for the ring section and then R1+R2, Zs and insulation resistance for the entire circuit. I'd then add a comment to explain that it's a lollipop circuit hence the lower than normal little "r" results and also the cable sizes on the radial and ring sections of the circuit.
 
I must say Pete I cant really see any pro's in a lollipop circuit?

As for extending an extinct cooker circuit, like Voltz says, why not use 4mm and keep it as a radial? I think mixing a ring and a radial is potentially asking for problems (DIY homeowner isolates wrong circuit, not a recognised method therefore increases risk due to unfamiliarity etc) and at the least a headache when it comes to testing, especially if it is not as simple as the ring starting from the old cooker switch.

Unless there are very clear reasons for why a 'lollipop' circuit would be preferably to extending as opposed to a radial (I cant see any) then I personally think it would be best to have either a 'ring' or a 'radial', not both mixed.
 
I must say Pete I cant really see any pro's in a lollipop circuit?

As for extending an extinct cooker circuit, like Voltz says, why not use 4mm and keep it as a radial? I think mixing a ring and a radial is potentially asking for problems (DIY homeowner isolates wrong circuit, not a recognised method therefore increases risk due to unfamiliarity etc) and at the least a headache when it comes to testing, especially if it is not as simple as the ring starting from the old cooker switch.

Unless there are very clear reasons for why a 'lollipop' circuit would be preferably to extending as opposed to a radial (I cant see any) then I personally think it would be best to have either a 'ring' or a 'radial', not both mixed.


That's because you're a electrical trainee, you can't see any further than what's covered in BS7671 and the picture book OSG and the like!!
 
I must say Pete I cant really see any pro's in a lollipop circuit?

As for extending an extinct cooker circuit, like Voltz says, why not use 4mm and keep it as a radial? I think mixing a ring and a radial is potentially asking for problems (DIY homeowner isolates wrong circuit, not a recognised method therefore increases risk due to unfamiliarity etc) and at the least a headache when it comes to testing, especially if it is not as simple as the ring starting from the old cooker switch.

Unless there are very clear reasons for why a 'lollipop' circuit would be preferably to extending as opposed to a radial (I cant see any) then I personally think it would be best to have either a 'ring' or a 'radial', not both mixed.

Re read post #8
 
That's because you're a electrical trainee, you can't see any further than what's covered in BS7671 and the picture book OSG and the like!!

Not sure why, but I expected more from you E54.

My boy lollipop , Millie small. lol

:smile5: I've just played that to my boy and he loves it, plays it over and over again!!!!

Re read post #8

I did see that Murdoch, but I would have thought x2 4mm fit in most sockets. I generally use crabtree and sometimes MK which both accommadate x2 4mm. However, if Wickes dont accommadate them I guess a lollipop is an option, but I personally would want to try and avoid it.
 
Last edited:
i would not test / record a lollipop circuit as a ring as only 1 set of conductors are at the CU , therefore at the circuits origin , it must be a radial.
And trying to separately record 2 sets of results for the ring and radial parts wont lead to much clarity in the report.
However i may conduct end to end continuity tests of the ring part to ensure proper construction , but would ultimately still record it as a radial
 
To add to my original post regarding Hybrid circuits, and having read the responses, one in particular peeked my interest, I think it was Eng54, where I think he said something along the lines of "just because it's not in BS7671 or the OSG doesn't make it a non compliant arrangement" if I have misread that then I apologize. but it does raise the question, if and I say if, because, as I said my personal thoughts are not in question, why doesn't the IET recognize these arrangements and include them in their publications?

I can hear the sighs now " because they are a bunch of dinosaurs etc etc, but it will be interesting to hear your thoughts.
 

Reply to Hybrid circuits in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top