P
Phoenix
Hi, not been here for a few months and my first visit back is asking for advice, sorry but I need my sanity back!...
This is in relation to installing a new CU. As well as the CU and a couple of other jobs I have to sort out the supply cable to the shed & garden. The supply is a TNC-S. The shed is currently supplied through 6mm SWA from the house, that is in turn supplied by 2x2.5mm cables (:whatchutalkingabout) from the existing CU and a 32A MCB. The total cable run is 25m. The EXISTING Zs in the shed sockets is 0.31 and the RCD in the CU trips well within time (don't have the exact times to hand, sorry). In the shed itself is a 3036 board with 5A for lights and 32A for sockets.
I am proposing to run T+E from the new CU to a JB on the outside wall then pick up the existing SWA. There is no way SWA will be entertained inside the house and even if it was some of the bends needed to reach the CU may not be achievable with it. In the shed itself I will install a 20A power circuit and 6A lighting. From the JB I will also run external sockets through a 13A FCU. As there is a lighting circuit in the shed I am intending to use 10mm T+E (10m) to the JB, then 15m of 6mm SWA giving a voltage drop of 4.57v so within the 3% (I have ignored diversity as there could be a few things drawing current at the same time so using worst case). Installation method will be Clipped Direct (possibly buried for SWA). I am protecting this with a 40A 30mA RCBO in the main CU, and will change the CU in the shed to MCB's.
Now to the part when my brain kicked in and I started getting all hyperthetical so I'm throwing this out there...to maintain safety the shed lights and sockets should, ideally, be on a split load CU but that seems massive over-kill. My worry is that if the RCBO trips at night, there is potential danger in trying to get out of a cluttered shed in darkness and stagger back up to the house to re-set the RCBO. So now we are left with necessity for discrimination if we are to install RCD's in the shed...can you get time delayed RCBO's? Would that still comply in protecting the 10mm T+E inside the house (buried cables)??? How would you achieve diversity with RCD's?
My solution - unless I hear differently on here - is to utilise the RCBO for protection and just install a simple 4-way CU in the shed with a main switch and MCB's; if the RCBO trips then it will have to be a short walk! To maintain safety I will add a non-maintained LED emergency light; they're cheap enough!
Over to to you all and I'm off to my bunker!
does the T/E from the CU to the SWA need RCD protection? if not buried in wall < 50mm deep, the it don't. then you could RCD in the shed. division of circuits in the shed is not necessary. fit an RCD and 3 MCBs... as sparty,s post, fitting a EM in the shed would be a good idea either way.
hahahahaha lmfao..............classic mate it really is whether your serious or pulling the pee...........cluttered shed in darkness hahahahahaha
Telectrix - yep, the 10mm needs protection in a thin partition
44ALLAN - I based that on personal experience!!! Glad you got a giggle!
can you not find a different route for the T/E, avoiding the thin partition? if not, then back to RCBO in house and fit a non-maintained LED EM. cheap as chips. about £14 squid.
Telectrix - not really; the CU is mounted on it! But I appreciate the thought. I have to use an external FCU as the sockets are to be mounted at the 'house' end of the garden, so saves a double run of SWA
OK, then. you can get a garage board for 20 odd squid. replace RCD with a D/P switch and put the RCD into your van stock.
Well c'mon ffs what did you expect................go to the pub or watch the telly in the house when it gets dark lol :)
There is an easier way,just keep the rake in the garden,that's the only thing in the shed that ever gets you.ouch!
Emergency light seems super, good thinking. I'd be a happy customer if you considered my safety like that.
How big is this shed?...
Emergency lighting and split loading in a shed seems like your over thinking it to me!...
It's about 15 ft sq with a car port adjacent but at a lower level so lighting at night is important. I know I'm overthinking it, that's what the thread's called! BUT...sheds and garages aren't exempt the regs. I know everyone just lumps lights and power on the same RCD but is that right? It's a hyperthetical question, really, as I intend to install the Emergency Lighting, but how would you satisfy the regs with regards to danger? Lights and power out together??? Only a thought...
I think I'm over thinking this!
Thread Tags
Tags Tags
thinking
Phoenix,
Phoenix,
TrueNAS JBOD Storage Server