DomSal

DIY
Joined
Jun 8, 2021
Messages
6
Reaction score
0
Location
Reading
I have a 4mm2 armored cable going from the CU in the house, under the drive and into the garage. The breaker for this is a 16 amp type B. I want to have 2.2KW planer machine in the garage that has a 16 amp plug whilst also keeping three existing double sockets in the garage. The three double sockets are currently daisy chained (radial connection?) using 2.5mm2 cable.

Should I have another CU installed in the garage that is fed by the existing armored cable and have the new 16Amp socket on a separate breaker (type C breaker is recommended by manufacturer)? The lighting and sockets could then be on their own breakers too.

Should I (can I) increase the breaker in the house CU and by how much?

Should the socket wiring should be upgraded to 4mm2 as it is not in a ring?
 
Should preface this by saying I’m not fully qualified yet - just waiting for nvq 3 from my employer!

But rcd discrimination would ensure garage trips first if there’s a fault there no? Correct me if I’m wrong !
Nope

Why would any particular rcd go?

In effect you have two devices in series, both operate at 30mA with the same time setting.

If anything, the upstream one is likely to operate first.
 
RCDs trip at values below 30mA. It’s just a maximum.

The ramp test of an rcd tester gives the actual threshold.
Some are only 19mA…. So whichever “30mA” rcd has the lower threshold, will trip first.

However… if the fault is substantial… it could be both.
 
I would personally add a rcd in the garage cu even if the house db has one. Saves the hassle of the entire house loosing power.

No it doesn't,
There are two reasons why the industrial 16A socket is not permitted in residential,

The regulations do not allow them for household use, but that's not the same as not being permitted in a domestic installation.
 
553.1.201

Every outlet for household shall be shuttered and preferably bs1363

(Paraphrasing as I haven't got my book to hand)

It's the lack of shutters on a 16A outlet that is prohibited.
16A socket has a shutter - a big blue spring loaded one, albeit a manually operated one.
Depends on the exact wording of the reg.
 
16A socket has a shutter - a big blue spring loaded one, albeit a manually operated one.
Depends on the exact wording of the reg.
Having looked this up now.... 553.1.201 says "Every socket-outlet for household and similar use shall be of the shuttered type, and, for an AC installation, shall preferably be of a type complying with BS1363" - so exactly as @Julie. said (thank you....). However what I'm now finding curious is that there doesn't seem to be an exception for those with interlocks either.

That said, 553.1.5 (iii) DOES allow outlets to BS EN60309-2 for special purposes where danger would arise or it is necessary to distinguish the circuit.
 
Having looked this up now.... 553.1.201 says "Every socket-outlet for household and similar use shall be of the shuttered type, and, for an AC installation, shall preferably be of a type complying with BS1363" - so exactly as @Julie. said (thank you....). However what I'm now finding curious is that there doesn't seem to be an exception for those with interlocks either.

That said, 553.1.5 (iii) DOES allow outlets to BS EN60309-2 for special purposes where danger would arise or it is necessary to distinguish the circuit.
Interestingly the definition of household is as follows : a house and its occupants regarded as a unit
So if the socket outlet is in a workshop at the property separate to and not part of the "household" then does this reg apply? So would this fall under the "special purposes" definition?
 
Interestingly the definition of household is as follows : a house and its occupants regarded as a unit
So if the socket outlet is in a workshop at the property separate to and not part of the "household" then does this reg apply? So would this fall under the "special purposes" definition?


It does indicate "or similar ", in principle I see it as either falling into household/residential.. or commercial/industrial.. or perhaps public.

Only commercial/industrial are regarded as having trained persons, so it's understandable that these are the only area where not having shutters or proper prevention of access to live conductors would be acceptable.

Anywhere where untrained persons can access I think implies the extent of protection described by this regulation, so sockets in a garden, garden shed/workshop/home office to me ought to be regarded as household.

In our own home workshop (husband's hobby) with lathe, Mill etc I have fitted interlocking outlets.
 
All this about interlocking 16A sockets…. But caravan owners, who are mostly untrained general public type people are expected to plug into whatever socket is at hand.

There are pre-made hook up leads with no interlocking sockets, and even 13A to 16A adaptors for plugging in at home.
 
All this about interlocking 16A sockets…. But caravan owners, who are mostly untrained general public type people are expected to plug into whatever socket is at hand.

There are pre-made hook up leads with no interlocking sockets, and even 13A to 16A adaptors for plugging in at home.
There was a change with the 18th. 16A site sockets are now required to be switched and interlocked, so any unswitched are now C3 on an EICR.
 
Should preface this by saying I’m not fully qualified yet - just waiting for nvq 3 from my employer!

But rcd discrimination would ensure garage trips first if there’s a fault there no? Correct me if I’m wrong !
Just going back to this. You cannot discriminate RCDs in the same way as you may be able to do with MCBs (and even this ain't easy).
Yes you could have a number of RCDs in a row with decreasing trip currents. but let's look at a simple example.
A 100mA RCD at source, and a 30mA RCD in the outbuilding.

Yes, it is true that an earth leakage of, say, 60mA would trip the 30mA but shouldn't trip the 100mA, BUT in the real World this doesnt happen. You usually get a big wolloping earth fault when you scythe through a mains cable and both RCDs trip because the instantaneous earth fault is more than several amps!!
The only reliable way to discriminate with RCDs is on the basis of TIME.
So you install a Time-delayed RCD nearer the source (they are called type S). The time-delay varies, and sometimes is adjustable. typically an S-type RCD has a time delay of between 150ms and 500ms. An earth fault of any magnitude will trip the standard RCD (typically within 40mSec). The S-type will stay in play.

This is another reason why it is better not to feed a submain (eg to a garage CU) directly from an RCD-protected MCB. Better to provide the circuit from a non-RCD protected way, or - even better - from a separate switch/fuse, then you dont trip the freezer when a mouse dies in the garage.
 
There was a change with the 18th. 16A site sockets are now required to be switched and interlocked, so any unswitched are now C3 on an EICR.
That’s only in specifically mentioned uses though, like caravan parks etc. I think the general concept of ‘industrial’ outlets in a domestic situation just hasn’t occurred to anyone?
 
From my earlier example, a 13A plug to a 16A socket (no shutters) for a caravan as an example…. Ok, the holes are bigger… but could be the same argument for the “figure 8” leads for radios and tvs… in fact, IEC leads for computers as well.

Once plugged in, it is possible to stick a metallic object into the socket end holes.



A bit off - direction to the original question…. In which case a 16A interlocked socket on a dedicated 16A radial. Not on the rfc with regular 13A
 
That’s only in specifically mentioned uses though, like caravan parks etc. I think the general concept of ‘industrial’ outlets in a domestic situation just hasn’t occurred to anyone?
Absolutely!

The problem is that when regulations are written, they tend to start from a "common sense" thinking.

Unfortunately people just try to find technical ways around them; interpreting them in a way that allows themselves to implement something that realistically ought not be done "the regs say red isn't acceptable, so it's OK to use cherry as it isn't technically red"

As such the regs end up chasing what has been done rather than catching it before it happens.

Three sayings come to mind:

Making things foolproof is impossible as fools can be very inventive.

Common sense, is neither common, nor sensible.

Yosemite Park ranger:
The problem with designing suitable waste bins, is there is considerable overlap between the average bear, and the stupidest human visitor
 
The problem is that when regulations are written, they tend to start from a "common sense" thinking
Absolutely, and I think it can work both ways. Some people find every possible way to reinterpret the regs to try and avoid something they don't want to particularly do for what ever reason. On the other hand, some people interpret the regs in a way that everything is black and white and that anything slightly askew is deemed unacceptable.
Then you have those (the ones with common sense) that use the regs for their intended purpose in that they are a guide to the minimum requirements deemed necessary to ensure installations are done to a common safe standard. There will be on occasion however, where some thought into the intended application/use of the install needs to be considered and what potential risks could be factors. The regs though, no matter how profound and detailed will not be able to cover all circumstances, this is where the installer needs to use their noggin and apply some sense.
 

Reply to I want a 16 amp socket in the garage with 3 double sockets in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
534
  • Question
Yes you will need to install # 4 wiring times 4 for your 2 hots, 1 neutral and 1 equipment ground. As for keeping the grounds and neutrals...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top