Hi guys
Came to do the testing on small bathroom lighting job today and I was confronted with this old piece of scrap iron.
I’ve never come across one of these before, so I’m asking you guys for confirmation of what I think what it is I’m looking for the type and BS number and amperage, so I can fill out my certificate, my thoughts are it’s a Bs 3036 semi enclosed rewire able fuses and guessing the fuse wire has been upgraded in the past from 30 amp to probably 60 amp.
I’ve already told my customer that they need to contact Electricity North West to have the head unit replaced as soon as possible for two reasons, the Bitumen has tracked back into the head and the live fuse is fully enclosed in the bitumen at the bottom and cannot be removed and the second reason it’s a fused neutral supply that’s no longer allowed be installed.
Cheers
Lee
Came to do the testing on small bathroom lighting job today and I was confronted with this old piece of scrap iron.
I’ve never come across one of these before, so I’m asking you guys for confirmation of what I think what it is I’m looking for the type and BS number and amperage, so I can fill out my certificate, my thoughts are it’s a Bs 3036 semi enclosed rewire able fuses and guessing the fuse wire has been upgraded in the past from 30 amp to probably 60 amp.
I’ve already told my customer that they need to contact Electricity North West to have the head unit replaced as soon as possible for two reasons, the Bitumen has tracked back into the head and the live fuse is fully enclosed in the bitumen at the bottom and cannot be removed and the second reason it’s a fused neutral supply that’s no longer allowed be installed.