Identify this head unit | Page 4 | on ElectriciansForums

Discuss Identify this head unit in the UK Electrical Forum area at ElectriciansForums.net

leebut

-
Joined
Jun 5, 2013
Messages
147
Reaction score
63
Location
Bury
Hi guys


Came to do the testing on small bathroom lighting job today and I was confronted with this old piece of scrap iron.

I’ve never come across one of these before, so I’m asking you guys for confirmation of what I think what it is I’m looking for the type and BS number and amperage, so I can fill out my certificate, my thoughts are it’s a Bs 3036 semi enclosed rewire able fuses and guessing the fuse wire has been upgraded in the past from 30 amp to probably 60 amp.

I’ve already told my customer that they need to contact Electricity North West to have the head unit replaced as soon as possible for two reasons, the Bitumen has tracked back into the head and the live fuse is fully enclosed in the bitumen at the bottom and cannot be removed and the second reason it’s a fused neutral supply that’s no longer allowed be installed.

[ElectriciansForums.net] Identify this head unit
[ElectriciansForums.net] Identify this head unit
[ElectriciansForums.net] Identify this head unit

Cheers


Lee
 
We can’t pull the fuses, I’ve only ever done it a handful of times and that was for real emergencies to avoid disaster.

Our island is only 36 miles x 12 so doesn’t take long for them to attend site..
Trouble with sparks pulling fuses and re-tagging is that it is open to abuse
Can’t see the problem with a registered spark being able to pull a cut out and re sealing using a registered numbered vinyl label similar to what some of the DNO use now, basically a registered installer gets an amount of numbered labels assigned to him and has to send a DNO notification with that seal number on it after the works carried out.

It makes sense for safe isolation of a supply which is in the safety at work act!!
 
In a perfect world it makes sense but there are too many rogues out there who could potentially use it to get free electricity..

It’s just too much hassle for them to put a system in place to allow us to pull fuses..
As far as they are concerned, apart from extreme circumstances there is no need for us to pull fuses..
If say we do a board change and you don’t want to do the tails live then we can arrange for them to pull fuse prior to works commencing
 
This happened to me a few months ago neutral fuse. I contacted the DNO immediately and advised the Landlord to shut off the power with a danger notice.

Was it dangerous in ways other than having a fuse in the neutral? If that was the main concern, I would not consider it worthy of isolating the system. The presence of a fuse in the neutral as well as the line is only a latent hazard, if someone does not perform safe isolation when the system appears dead due to the neutral fuse having blown, which itself is very unlikely. It is a world away from having fuses in the neutral instead of the line in which case there is no earth-fault protection.
 
I thought the fact the cutout was Cast iron with Ceramic fuse holders was a bigger concern.
Weren't they supposed to have been changed years ago under direction of the Regulator?

When the DNO come out to the O.P, depending on how much room there is around the cutout to work it's quite likely they'll dig up outside and cut the service before they touch the Cutout.
 
Whenever I come across a problem with a service head I ring ENWL myself, explain I am an electrician on site and tell them what the problem is. I then arrange a date and time with ENWL to attend the property. I make sure I am there and will supply and fit the isolator to the back board before they come (all chargeable to the customer) ENWL will then fit the tails into that and I will then reconnect the CU to the isolator, never had a problem with this arrangement and usually the guys from ENWL are quite accommodating with this arrangement.
 

Reply to Identify this head unit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top