Greetings.
I tested an rfc and recorded the following results:
r1 = 0.62
rN = 0.89
r2 = 1.45
The difference in r1 and rN indicate loose connections so I checked all the sockets (bar one) on the ring which revealed two loose connections.
The rfc now tests as follows:
r1 = 0.58
rN = 0.59
r2 = 1.45
The measurements indicate a 80 metre circuit of 2.5mm^2 csa.
I've checked every socket in the dwelling except one which feeds a waterbed and is inaccessible. So I told the customer that I have some homework to do before I can issue certification.
BUT, I hadn't realised that it could be 2.5/1 t&e in which case the measurement of 1.45 (remaining constant) is correct.
I don't have a micrometer to measure the cpc so how do I confirm the cable conductor's csa? ... and if it's 1mm^2 cpc is that okay?

The wiring is about 25 - 30 years old.
 
what you could try is connect L to E on one side of the ring and leave the other open at the board, check the R1 R2 readings at the sockets nearest then move further along until you notice any major jump , if its a gradual increase on all then o/k ,
 
what you could try is connect L to E on one side of the ring and leave the other open at the board, check the R1 R2 readings at the sockets nearest then move further along until you notice any major jump , if its a gradual increase on all then o/k ,
to make this quicker, wire a plug with a bit of flex from it going to connector strip.

this makes it quick to a quick check without removing fronts (very useful if there if there is a dead short somewhere)

or if you have a multimeter etc with non gs38 leads just shove them in the socket
 
I would compare a bit of new cable with the old , for the earth wire size , if you have test leads to a plug then you won't need to remove the socket fronts ...

If you have done this then as shanky says if Zs is good at end of circuit then its o/k
 
I would compare a bit of new cable with the old , for the earth wire size , if you have test leads to a socket then you won't need to remove the socket fronts ...

Thanks again R G,
I started to doubt myself and stopped thinking clearly.

Is it satisfactory to have a 1mm cpc on a rfc protected by a 32A type b breaker?
 

Reply to Identifying csa of t&e in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
426
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top